    Emergency battery backup retrofitted in light, plus light feed from emergency backup?

    Why would you have a EM battery back up retrofitted, and plus it's fed for from emergency back up inverter? Never seen a battery backing up a battery before. Some new code? Thank you for your help.
    "The bitterness of poor quality lingers long after the sweetness of a cheap price is forgotten"

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,761
    Probably somebody misinterpreted what they thought was required.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.

  3. #3
    Join Date
    Oct 2015
    Location
    Fort Wayne, IN
    Posts
    4

    Depends on time

    NFPA standards apply for emergency lighting standard. They have to meet a time standard, if the internal battery cannot produce the minimum light level over the time frame required, then a secondary immediate power source is required when line voltage is lost. So maybe they are trying to meet the requirement.

    As I don't seem to see the original post, I would be interested in seeing what the post said. I might even be able to help quote the exact requirement once I have the facts.

  4. #4
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,092
    Quote Originally Posted by zappy View Post
    Why would you have a EM battery back up retrofitted, and plus it's fed for from emergency back up inverter? Never seen a battery backing up a battery before. Some new code? Thank you for your help.
    What is the nature of the "emergency backup inverter"? Is it just a centralized battery bank connected to the emergency lights?

    I also don't understand why someone would do this. A stand-alone emergency light or combination emergency/exit light is designed to give the required 90 minutes of light at the proper level. Usually they'll deliver a lot more when the batteries are new and in good condition.

  5. #5
    Join Date
    Mar 2009
    Location
    NYC
    Posts
    41

    micro inverters

    Quote Originally Posted by gadfly56 View Post
    What is the nature of the "emergency backup inverter"? Is it just a centralized battery bank connected to the emergency lights?

    I also don't understand why someone would do this. A stand-alone emergency light or combination emergency/exit light is designed to give the required 90 minutes of light at the proper level. Usually they'll deliver a lot more when the batteries are new and in good condition.
    Because crazy designers don't want to see "ugly" EM fixtures mixed with pretty lights ... Philips "Bodine" 20W, 100/250/400W or "COOPER LIGHTING - SURE-LITES " up to 2000W micro inverters allows to convert ordinary lights in to EM. So, "any" fixture or group of fixtures can serve both e.a night lights or EM light during the blackout. We have this spect for the commercial project "fancy club space (part of amenities for the residential building in NYC) I stared doing some research and This brings questions like, 1. How should those EM fixtures be identified ?, 2. Since the unit (inverter ) is remotely installed - where should be the test button /indicator installed -in the closet or out in space where the lights are? 3. What about disconnecting means -should two be provided one for feeder and one for secondary (EM /110V ) etc. If someone used this already your input would be appreciated.