A feeder run(5 sets #600mcm) starts on the 1st floor goes horizontal about 80' to a riser where it then goes up about 200'. Would there more than likely be a splice where it transitions horizontally to vertically? I'm thinking a box with splices at that point. Thanks
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I would not expect to see a splice in that run.
Make sure you take a look at 300.19 if you have a 200' vertical rise.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
My money would be on no splice.

I agree. Unless there were many bends in the horizontal I would make this in one pull but not knowing the entire run makes it's really difficult to properly answer the question.
 