Thread: Current limiting in 3 phase 240v computer application

  1. #21
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,183
    for work of the scope is a PE involved?
    a mech, elrc, etc
    alot of money is being expended and it sounds like you are being paid to do engineering
    that may not be legal in PA

    the ai aspect sounds weird
    more like bitcoin
    no major universities or private research institutions afaik in scranton pa

    I would advise you to retain professional assistance
    for your sake and the clients
    it sounds like you are out of your depths since if you weren't you would not be asking such fundemental questions on the internet
    you would have local resources with which to consult: engineers, suppliers, contractors, etc



  2. #22
    Join Date
    Apr 2016
    Location
    Raleigh, NC USA
    Posts
    363
    Quote Originally Posted by quantboy5 View Post
    No UPSs... These are application specific machines designed to crunch matrix calculations -- they can and will fail - and this will not cause a problem with the main objectives. Therefore no UPSs will be included.
    If you are not installing UPS s make sure you have some type of surge protection either in your custom pcb or off the shelf PDU.

    Either way check back in and let us know how the project goes. Definitely interesting!

  3. #23
    Join Date
    Nov 2017
    Location
    scranton, pa
    Posts
    7
    Thank you everyone for your replies! Some great insight here -- project is going to engineering firm for review and prints, per complexity of project.

  4. #24
    Join Date
    Nov 2017
    Location
    scranton, pa
    Posts
    7
    Quote Originally Posted by Ingenieur View Post
    what?
    if you have an enclosed space with btu's being released into it they must be removed
    does not matter what the source
    if what you are saying you will ventilate with unconditioned air you will destroy the equip due to humidity
    on a warm day blowing in 90 deg air and the room at 100 little temp drop will occur
    tis will be the first 1.2 mw data center I've seen without mech cooling
    and I've seen a bunch
    temps could exceed 120 deg
    Ouch! That does make sense. Passing it along to the client.

  5. #25
    Join Date
    May 2010
    Location
    Inside the Beltway
    Posts
    615
    Quote Originally Posted by quantboy5 View Post
    Customer wants to have 60 machines powered by December 31st... 300 machines by feburary 31st (2000A @240V 1 phase)... and 1000 machines by August 31, 2018 (6000A @ 240v 1 phase or 2000A @240V/3phase)

    If not a Bitcoin miner.....it's a Beowulf Cluster.