Page 3 of 3 FirstFirst 123
Results 21 to 28 of 28
Thread: Pulling Wire
  1. #21
    Join Date
    Feb 2003
    Posts
    148
    Underground conduits will usually be full of water especially if going from building to building.
    If you have to blow the water out to get the pull rope through then there may be a big mess to clean up.
    Need to factor the labor time for it, even if it is just the poor apprentice.
  2. #22
    Join Date
    Apr 2005
    Atlanta,GA
    Posts
    5,596
    Quote Originally Posted by Unbridled View Post
    The primary reason I run as much conduit under the slab is the total length of the up-coming wire pull.
    The drops from conduit installed from above are longer than the stub-ups out of the slab to a receptacle for example.
    I try to run as much as possible under the slab. No one cares if the PVC is running at angles, unlike exposed conduit runs.
    For sure it's better to put as much as possible in the slab. You can save on both labor and materials.
    I thought the OP was asking if say a 400 ft pull of cable would be easier underground or overhead. If the length of the cable to be pulled is the same I wouldn't want to bet on which will go faster .
    The 95% of people that you can't trust give the other 5% a bad name.
  3. #23
    Join Date
    Jul 2005
    Posts
    776
    Quote Originally Posted by mstrlucky74 View Post
    Not for wire pulling. That's why I'm asking. Always been told there's a labor savings when installing conduit in a trench or on the floor as opposed to overhead which makes sense but never got info on wire pulls being different.
    So if someone gave you a response that they experience a 20% labor saving for pulling underground, are you going to discount your labor units for those runs? That would be someone's opinion.
    Maybe they have kept really good historical data in their shop for wire pulling. But that's their data based on their research
    You're overthinking again....throughout a given job, there will be more difficult or very easy pulls....it all averages out. You win some and lose some.
    I don't like discounting or adding labor for items that don't show adjustments for that task (unlike conduit where there are several levels of difficulty)
  4. #24
    Join Date
    Sep 2012
    NJ
    Posts
    1,796
    Quote Originally Posted by cdslotz View Post
    Understood and agree. I was asking because you guys seem to be at the top of your games and if 10 people responded and 8 said it usually easier to pull underground than overhead(all circumstances being equal except where the conduit is being installed...and yes more than likely the conduit will be PVC in grade and not PVC in a building so that would be a constant different) I would have it consider putting in a discount...especially if I have 15,000'.
  5. #25
    Join Date
    Apr 2007
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,311
    not a good idea to discount wire pulling.
    very, very bad idea.
    if you have a problem with a pull, and everyone does
    at one time or another, usually what happens is it might
    get repulled, and you'll eat the cost of the wire.
    i walked in on a data center, was the night shift foreman,
    and day shift tried to pull in 400' of 500 mcm copper.
    with a smaller ground.
    off a wemco reel.
    without pulling the locking pin on the sheaves out before
    starting the pull.
    when i showed up, most of the wire was in a huge ball,
    in the parking lot. all snarled. they'd spent all day with
    it, and still didn't understand what was wrong. by then,
    it was a bit late. imagine a 20' ball of wire weighing about
    a ton. now, try to untangle it, in the dark. don't nick that
    insulation, hear?
    they ordered a new wemco full, and repulled with that.
    1,600' of 500 mcm, and 400' of 4/0 copper. they paid
    us to cut it up and strip it for scrap.
    how's that discount feeling now?
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~
  6. #26
    Join Date
    Sep 2012
    NJ
    Posts
    1,796
    Quote Originally Posted by Fulthrotl View Post
    off a wemco reel.
    starting the pull.
    insulation, hear?
    Wow. But that seems like a rare instance.
  7. #27
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,331
    Your on ladders and lifts when pulling wire?
    Depends on the application. Even a run that is mostly underground could run to a location where you need ladder/lift to access an end of the run.
  8. #28
    Join Date
    Mar 2003
    New York
    Posts
    763
    Underground, like in a manhole?
    You would need a sniffer, safety stand/harness, pumps, etc..
    Off the same concrete floor as overhead run, I would say underground would be faster but no discount faster.
Posting Permissions
  • You may not post replies
  • You may not edit your posts
