Thread: Relay-controlled vs. direct-wired lighting and NEC compliance

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Join Date
    Jan 2016
    Location
    Biloxi MS USA
    Posts
    8

    Relay-controlled vs. direct-wired lighting and NEC compliance

    I'm planning the wiring for a future house and wondering if I can comply with NEC by installing radio- and internet-controlled Sonoff relays at my ceiling and wall lighting outlets?

    This means there will be no wiring to any wall switches, and in fact there will be no traditional switches used to control the lighting in the entire house. Instead a wifi- and rf-enabled relay will be installed at each lighting outlet, and these relays will be controlled remotely. This will enable all lights to be switched on and off via several different methods:

    1- A smartphone app which has the ability to: (1) switch each light on and off individually; (2) switch pre-defined groups of lights on and off; (3) set timers that turn lights on and off on a regular schedule. This control method will work from any location where the smartphone has an internet connection.

    2- Non-traditional "remote control" wall switches that are simply stuck on the walls (with double-stick tape) wherever desired, including typical locations such as near doorways, and in non-typical locations (near the toilet, shower, next to the bed, etc.).

    3- Portable key fobs which send a RF 433Mhz radio signal to "flip the switch" at the correct Sonoff light relay.

    Other than possible NEC non-compliance, are there any reasons why this shouldn't work?

  2. #2
    Join Date
    Jan 2016
    Location
    Biloxi MS USA
    Posts
    8
    Correction: The Sonoff units are not relays, they are remote-controlled switched. Sorry about that.

  3. #3
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,703
    171201-1152 EST

    Will this equipment work 50 years from now? Do you want some outsider to control your lights or other loads? Do you want your circuits "jammed" so they do not work? What happens if the Internet is down, or WiFi is not operating?

    .

  4. #4
    Join Date
    Jul 2013
    Location
    Arcata, CA
    Posts
    384
    What happens if the power flickers off and on? Will they retain their status, or go to a default?
    If I were going to do this (no way would I) I would put all the controls in one or two locations so if a different technology is chosen later, they can be more easily changed.

  5. #5
    Join Date
    Jan 2016
    Location
    Biloxi MS USA
    Posts
    8
    Interesting thoughts, thanks. I agree with these concerns so here's an alternate question:

    Is it possible (legal) to run 5vdc or 12vdc power via cat5 cable from normal wall light switches to low-voltage relays at my lighting outlets? I would still have to change faulty relays when they fail, but are there other cons to this approach?

  6. #6
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,703
    171291-1501 EST

    Consider GE RR type relays. These are bistable electromechanical and operate at a nominal 24 V. Put the relays in gang boxes and not at the fixture. All hard low voltage wiring. Dimmers are a separate issue.

    My RR relays are over 50 years old and I have had few problems.

    .

  7. #7
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,384
    Quote Originally Posted by owkaye View Post
    Interesting thoughts, thanks. I agree with these concerns so here's an alternate question:

    Is it possible (legal) to run 5vdc or 12vdc power via cat5 cable from normal wall light switches to low-voltage relays at my lighting outlets? I would still have to change faulty relays when they fail, but are there other cons to this approach?
    That's similar to what's already been done with the old smart home technology. All your switch legs go back to a panel and cat 5 goes out to all your switch locations.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.