Page 3 of 3 FirstFirst 123
Results 21 to 28 of 28

Thread: Semantics of "Area Classification" and who should determined Areas

  1. #21
    Join Date
    Mar 2013
    Location
    USA
    Posts
    1,094
    I have looked for training focusing on NFPA 497, RP 500, or focusing on NFPA 70 Article 500, but have not found anything.
    Time is of the essence, and I am low on essence. ~ Graham Hill

  2. #22
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,076
    It may be of some interest that the members of the Technical Committees that edit/author the various Standards that I mentioned earlier in Post #16; i.e., CMP 14 (NEC Arts 500 to 516), NFPA Technical Committee on Electrical Equipment in Chemical Atmospheres (NFPA 497) and API Subcommittee on Electrical Equipment (API RP 500) virtually all have "electrical" backgrounds. The API SOEE exclusively in fact.

    I've said many times before Hazardous (Classified) Locations is NOT rocket science. It isn't trivial either; it DOES take some thought but any relatively competent individual can learn it.

    NFPA occasionally offers training for Hazardous Locations - every instructor I've known is "electrical".
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  3. #23
    Join Date
    Mar 2014
    Location
    South Florida
    Posts
    163
    I work in wastewater and water plant design. Most (9/10) times we (Electrical/I&C) are tasked with identifying classification types and areas, showing them on our plans. It impacts electrical/instrumentation installation costs more so then any other, with exception to perhaps HVAC/mechanical having to add ventilation systems. I think for this reason we often lead the discussion on the subject.

    We have made a push to make it a design team discussion with mixed results.

  4. #24
    Join Date
    Jul 2017
    Location
    Alberta, Canada
    Posts
    27
    They can be called "Hazardous Area Classification Drawings", "Electrical Area Classification Drawings", or anything similar. I prefer "Area Classification" because new standards recognize that non-electrical equipment can cause ignitions.

    Most guidance on risk analysis says that such activities are best done with a multidisciplinary team (electrical, mechanical, HVAC, process, as appropriate), led by someone with appropriate experience. This (obviously) applies to area classification, but is (equally obviously) not always practical.

    Area classification is generally the owner's responsibility.


    I agree EEs are the ones often saddled with the responsibility of the area classification; I also agree they're not necessarily the best qualified.

  5. #25
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,076
    Quote Originally Posted by IntrinsicSafety View Post
    They can be called "Hazardous Area Classification Drawings", "Electrical Area Classification Drawings", or anything similar. I prefer "Area Classification" because new standards recognize that non-electrical equipment can cause ignitions.

    Most guidance on risk analysis says that such activities are best done with a multidisciplinary team (electrical, mechanical, HVAC, process, as appropriate), led by someone with appropriate experience. This (obviously) applies to area classification, but is (equally obviously) not always practical.

    Area classification is generally the owner's responsibility.


    I agree EEs are the ones often saddled with the responsibility of the area classification; I also agree they're not necessarily the best qualified.
    I have been mulling over how to respond to this and several of your other recent posts. It took me a while to realize you are in Canada - let me be clear, that's just fine.

    I must confess it has been nearly 20 years since I was actively engaged with the Canadian Electrical Code, Part I and the corresponding Hazloc issues. In my opinion, Canada had just adopted IEC Zones correctly; i.e., :whole hog". As I recall, "Divisions" were relegated to an "Annex". I don't know if that is still the case.

    The consequence though, is attempting to apply Canadian practices is just about as bad as attempting to us IEC practices, "straight out of the gate". The 60079 series, unless it has been ANSI/UL/ISA "sanitized" is meaningless in the US.

    There are many IEC practices I appreciate, but the US Zones and IEC Zones just aren't quite compatible.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  6. #26
    Join Date
    Jul 2017
    Location
    Alberta, Canada
    Posts
    27
    Hey Bob,

    At risk of hijacking this thread:

    As always, you are correct. Canada switched to Zones and put Division in Annex J of the CEC some time ago. (Although we only just got Zone dusts sorted in the latest edition.)


    Almost all IEC 60079s have been adopted by ANSI/UL and CSA by now. At least as far as equipment goes.

    Certainly (but not obviously), the various adaptations have no force outside of their relevant jurisdictions. So yes, EN and IEC are technically meaningless here.

    However, as they are all 97% harmonized, I think it's fair to say they are close enough to equivalent for the purposes of most conversations. So - in most cases - "IEC 60079" can legitimately be read as "ISA", "UL", or "CSA", as appropriate.


    Not to ignore the existing non-harmonized Div standards: NFPA 496, ISA 12.12.01, UL 1203, etc. There can still be stark differences.

    Fortunately, the NEC has had Art 505.1 and Art 505.9 for a while, making Div and Zone certified product substitute-able (within appropriate limits).


    Area classification is more fuzzy, IMHO.

    I've done more ACs than some, not as many as others, and was fortunate enough to get education.

    I'm currently of the opinion that any method will do as long as it's justifiable. So I'm perfectly happy to steal the best available guidance from any source.

    Since some of the European standards are ahead of NFPA in this respect, and thus may provide an appropriate way to reduce the size of classified areas, I don't hesitate to consider them. Others may disagree.

    Certainly, in areas where the NEC has specific definitions, I'll use those. Usually arguing against the NEC is a bad call. But it's legitimate to modify if you have sound engineering judgement.


    It will also be useful to know that I am primarily an equipment designer - PCBs, enclosures, and such - which makes me a standards guy, not a Code guy.

    As such, I do tend to skew towards design, standards and NRTLs, rather than installation, NEC/CEC and AHJs. I was hoping that perspective would prove useful to those few areas I may be able to comment on.


    In any case, if I seem to be confounding the "USA approach" with the "Canadian", "European" or "IEC" approach, it's intended only to be a convenient approximation. I would never try any kind of cross-jurisdictional approach, nor should anyone else.

    I would love to have the luxury of only having to consider a specific jurisdiction, but it's not in the cards for me. I'll try to be more specific in the future.

    Having said all that, I stand by my previous comments.

  7. #27
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,076
    The problem with Section 505.9 is that pesky "A" in Section 505.9(C)(2)(3).

    I was basically an electrical plant design engineer so classification practices are a major concern. I spent about a third of my career in IEC environments

    As I mentioned, there are several Canadian practices, like TECK 90, I like but it doesn't comply with the NEC. My suggestion to the API Subcommittee on Electrical Equipment eventually became Type MC-HL. I also like "Ex e" terminals for Division 2 and they were a standard in my "spec" days. FWIW I suggested to the main "Division 0" manufacturing advocate in the early to mid 90's what became Section 501.5. (I was even happy with using "straight" IEC "Ex")

    One major, but subtle, difference is there are no "ordinary location" location products acceptable in the IEC Zone system - even Zone 2. (That's where the pesky "A" came from originally)

    There are other significant differences, that I don't see being ironed out in my lifetime.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  8. #28
    Join Date
    Jul 2017
    Location
    Alberta, Canada
    Posts
    27
    It is indeed a pity we can't all (yet) get along.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •