    Bus duct VD calculation

    I'm calculating VD on a bus duct.
    The run is 400ft,
    At 275ft there is a meter bank another one at 350ft and lastly one at 400ft.
    With the various online calculators there are 2 options , distributed load & concentrated load.
    I'm thinking that I should be working of distributed load whereas others think I should be using concentrated load to the 1st set of meter banks & segmented loads after that.
    This makes a big difference as VD is halved if I can use the distributed load.
    Which table should I use?
    cmac1

  2. #2
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    385
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If you are being cost conscious, distributed is fine. Conservatively, you’d use concentrated at end of run.

  3. #3
    Join Date
    Jun 2003
    Posts
    6,940
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    to get the most accurate voltage drop, use the concentrated load and figure each section of bus duct individually, and add the results.

  4. #4
    Join Date
    Oct 2016
    Location
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    mcelweec

    "With the various online calculators there are 2 options , distributed load & concentrated load."

    Would you please post some "LINKS" or name the sites for a few of these calculators.

  5. #5
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MyCleveland View Post
    mcelweec

    "With the various online calculators there are 2 options , distributed load & concentrated load."

    Would you please post some "LINKS" or name the sites for a few of these calculators.
    http://www.eaton.com/ecm/groups/publ.../ct_152882.xls

  6. #6
    Join Date
    Oct 2016
    Location
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thank you

  7. #7
    Join Date
    Oct 2016
    Location
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ingenieur

    Have you used this program ?

    If you understand the inputs.....can you explain difference between cell B1 & B13 ?

  8. #8
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MyCleveland View Post
    Ingenieur

    Have you used this program ?

    If you understand the inputs.....can you explain difference between cell B1 & B13 ?
    'actual' B1 is your connected load
    'upsize' B13 (B10?) is if you want future expansion
    say your load is currently 1000 (actual), and it will be 1250 (upsize) in 2 years after expansion
    if no expansion or increase in load is planned actual = upsize

    play with it
    change inputs and see how it changes the results
    Last edited by Ingenieur; 12-23-17 at 12:53 PM.

  9. #9
    Join Date
    Oct 2016
    Location
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ingenieur

    Thanks again
    I am tinkering...here is a rub. If B13 is not a table value (Standard Size), then everything collapses.

    I will start with retagging a few things and adding some conditional drop downs.

    May I reach out again later ?

  10. #10
    Join Date
    Oct 2016
    Location
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Concentrated vs Distributed....division by 2.
    Guess I thought more options in the input selections were available.