User Tag List
Results 1 to 9 of 9
Thread: applying 110.14 (C)
  1. #1
    Join Date
    Feb 2015
    Millbrae CA, San Mateo
    Posts
    23
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    applying 110.14 (C)
    I am coaching one of my students who is preparing to sit for the California certification. She is using Tom and Tim Henry's 2014 exam preparation text. One of the chapter 2 (don't have it in front of me, but I believe it was this chapter) questions is what is the allowable ampacity for 4, 4/0 THWN copper conductors with an ambient temperature of 45 celsius. No terminal temperature rating is given. I told her that she had to use the 60 degree column as a starting point, even though THWN is listed in the 75 degree column. Accordingly, the calculation I suggested she use was (195)(0.80)(0.82). The result would then be 127.92, or 128. When we looked up the answer, the result was 150.88---151 amps. Clearly, the Henrys' starting point was 230 amps from the 75 degree column. In the absence of any information on terminal temperature rating, is it not true that one must proceed with the 60 degree column?
  2. #2
    Join Date
    Feb 2015
    Posts
    23
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    oops
    Duh. Just realized that given the 4/0 size of the conductors, one is directed to use the 75 degree column. Apologies for wasting everyone's time.
  3. #3
    Join Date
    May 2013
    Massachusetts
    Posts
    2,438
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ohmboyz View Post
    In the absence of any terminal rating specified, 60C is the default for 100A and less, while 75C is the default for everything over 100A. Even if the wire rating is higher. You may encounter a master statement at the beginning of the exam to default to the 75C column, since this represents what is most common in the field, but in the absence of such a statement, follow the defaults specified in 110.14(C).
  4. #4
    Join Date
    Feb 2004
    Posts
    660
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    4/0
    4. 4/0 THWN 45C IN CONDUIT = 197.6 AMPS.
  5. #5
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,617
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by domnic View Post
    The question assumes that the 4 conductors are all current carrying. (230*80%*.82=151)
    Rob
  6. #6
    Join Date
    Feb 2015
    Posts
    23
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    please show me your math
    Wondering how you got 197.6? Per the comment below, it was indeed four current carrying conductors. My bad I omitted that info. Accordingly, I believe the math goes something like (230) (.82)(80) (assumes 75 degree column---100 amps {110.14 (C)}given the size of the four 4/0's) which I believe leaves one with 150 +
  7. #7
    Join Date
    Mar 2014
    McKinney, Texas
    Posts
    1,471
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Greetings,
    The question gave you the size of the conductor which was clearly in the 75°C Column per 110.14(C)(1)(b) as well as the number of current carrying conductors which brings in Table 310.15(B)(3)(a) as well as the 45°C that brings in 310.15(B)(2)(a). As you concluded, you will start from the 75°C values due to those facts. Interesting note, we could have changed the THWN to THWN-2 and changed those values as well but alas it was only THWN being expressed.
    The 230A x .80 x .82 = 150.88 (151 Amps) is the THWN's new de-rated ampacity.
    But I see you already figured that out.
    Many times on exams do not assume what the logical answer would be but simply what the question is asking. While it is important to teach the student the real world aspects of electrical work, in the exam environment we only focus on what the test question is asking and simply solve the question.
    *All code responses are based on the 2017 National Electrical Code®[NEC®]
  8. #8
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,195
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MasterTheNEC View Post
    Greetings,
    Its one place where it seems experience may hurt. I've found experienced folks often take more into consideration in looking for an answer to a test question than is asked. For instance, taking the limitations of 240.4(D) into account when the question only asks about "ampacity"
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  9. #9
    Join Date
    Feb 2004
    Posts
    660
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    4/0
    MY bad I used THWN-2.
Posting Permissions
  • You may not post replies
  • You may not edit your posts