    Is liquid tight acceptable in a class1 div1 location?
    If I'm not splicing in a Tee condellet can i use a non explosion proof Tee with a seal off before it and after it?
  2. #2
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,542
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The straightforward answer to both questions is, “no”.
    LFMC is not a recognized wiring method for Class I, Division 1 in Section 501.10(A)(1).
    Section 501.10(A)(3) requires boxes and fittings to be approved for Class I, Division 1.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.
  3. #3
    Join Date
    Dec 2017
    Richmond Va USA
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for the straight forward reply.
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,054
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    As a straight forward answer no seems most appropriate. However there are some cases where it would be acceptable such as where IS circuits are used or even with a pressurized system. Based on the wording of your original question though I think the answer is no in your case.
    Bob
  5. #5
    Join Date
    Nov 2017
    Whg. WV USA
    Posts
    17
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I know this thread is a few days old, but there is liquidtite and liquidtite connectors listed fo Class 1 Division 1 locations. They make installing explosion proof lights and motors much easier.
    Steve
  6. #6
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,201
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sblk55 View Post
    Steve
    Steve,
    Do you have a link to the manufacture of this LFMC?
    Chris
  7. #7
    Join Date
    Feb 2003
    Illinois
    Posts
    23,908
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Steve
    If it is listed as LFMC, it doesn't matter what the listing says. The code rule prohibits the use of LFMC in Class I, Division 1 locations. Nothing in the listing can change that. Now if it is listed as something else, such as a "flexible coupling" that would be different.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  8. #8
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,957
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Note that it is perfectly possible to be listed as both. But far too expensive to be used just as LFMC.
  9. #9
    Join Date
    Nov 2017
    Whg. WV USA
    Posts
    17
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Sorry I do not have a link, we had the guys at Graybar get them for us.
    Steve
  10. #10
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,542
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Steve
    I imagine what you actually received was an explosionproof flexible coupling. [Section 501.10(A)(2)(1)] It is definitely not LFMC. Technically, it isn't even conduit; it is a coupling. The distinction from LFMC is the threads are an integral part of the factory assembly.