Page 11 of 12 FirstFirst ... 9101112 LastLast
Results 101 to 110 of 113
Thread: Vertical 300hp Well Pump Motor
  1. #101
    Join Date
    Feb 2013
    India
    Posts
    2,278
    Still the possibility of defective drive may not be ruled out because it is perpetually on start mode without shutting down under load.
    Quote Originally Posted by adamscb View Post
    What is also pretty odd is the status always says "Accelerating" and doesn't change to "Running".
  2. #102
    Join Date
    Apr 2015
    IL
    Posts
    156
    Pump was stuck...VFD acts like it should now. Still being able to run while under pretty much locked rotor conditions is incredible, in my opinion.
  3. #103
    Join Date
    Jul 2006
    Posts
    7,173
    Thanks for reporting back!
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  4. #104
    Join Date
    Jan 2016
    PA
    Posts
    4,530
    what was the issue?
    an object jammed in it?
    etc
  5. #105
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,053
    Quote Originally Posted by Ingenieur View Post
    what was the issue?
    etc
    Yes, how?
    Tom
    TBLO
  6. #106
    Join Date
    Sep 2008
    UK
    Posts
    10,565
    Excellent that you got a fix...........)
    One thing surprises me a bit. With a centrifugal load is the the motor cooling fan is normally shaft driven. With a locked rotor, you would lose that cooling altogether.
    Maybe you didn't run it for very long...
  7. #107
    Join Date
    Apr 2015
    IL
    Posts
    156
    The mechanic seemed pretty reluctant to tell me, all I know is that the shaft wouldn't turn by hand. They re-coupled it and were able to turn it by hand then.
    And as far as running it when it was stuck, we only ran it for maybe 10 seconds at a time. We knew something was wrong and shut it down immediately. I'm guessing if it was ran for an extended amount of time it would have tripped eventually.
  8. #108
    Join Date
    Sep 2008
    UK
    Posts
    10,565
    Or cooked...
  9. #109
    Join Date
    Apr 2015
    IL
    Posts
    156
    Quote Originally Posted by Jraef View Post
    The default setting of that particular drive is for it to attempt to stay running by driving down the frequency and lowering the current limit. If the user did not change that setting (and it sounds probable), that would completely justify what he is seeing. So really, what we DON'T know is why it is a perpetual state of overload. It cannot be that the motor is overloaded from flow, there is none. So it leaves a mechanical problem or a defective drive, and he has run the motor uncoupled from the pump with no issue. I'm going with a mechanical problem here.
    Jraef, thanks for this post, you were spot on with this. For ease of troubleshooting, do you think that this parameter should be changed to "Disabled", so something is forced to trip? I see pro's/con's for either way, either letting it trip out or reducing Hz/current to protect the drive, your thoughts?
  10. #110
    Join Date
    Jun 2003
    Posts
    9,053
    Jraef, thanks for this post, you were spot on with this. For ease of troubleshooting, do you think that this parameter should be changed to "Disabled", so something is forced to trip? In my opinion I think it should be left the way it is to protect the drive, but I'm not our backshift electricians working at 2am.
    How often is this likely to occur?