User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 11
Thread: System Grounding ok
  1. #1
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    System Grounding ok
    Attached is system grounding detail new service disconnect switch as shown for cell tower on building. See existing system grounding detail, single line diagram and elevation below. I am tying service disconnect switch to existing building system ground electrode. See both diagrams. Is it per NEC 2014 Article 250? Anything not per NEC 2014 Article 250?
    Attached Thumbnails Attached Thumbnails Click image for larger version.
Name:	System Ground.jpg
ID:	19174   Click image for larger version.
  2. #2
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,044
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    How are you feeding this new service? Is it a second service or are you bringing in another set of service entrance conductors? If so, this may change the size needed for your existing GEC and bonding jumpers.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  3. #3
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Their is new electric service from new electric utility transformer. Is it okay to splice at grounding rod as shown on grounding detail?
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,054
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    as long as the existing conductor from the rod to the steel is #4 Cu or larger I think it is OK.
    I am not sure the nomenclature used is correct though for the new wire coming from the new neutral bar. I think that is a GEC and not a bonding jumper.
    Bob
  5. #5
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by codequestion View Post
    Why go through the bother of that splice?
    Take the new GEC to building steel and connect.
    250.68. You already have jumpers to rods and water pipe.
    "Electricity is really just organized lightning." George Carlin
    Derek
  6. #6
    Join Date
    Jan 2009
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    I agree.
    Derek
  7. #7
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,054
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    Because the drawing says so.
    I agree this is code compliant.
    Just because a different way is code compliant does not allow one to do something that is not in compliance with the contract documents.
    Bob
  8. #8
    Join Date
    Jan 2009
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree, I would never not do an EE/contract spec.
    I thought OP was the designer. His third sentence seemed to imply this.
    Derek
  9. #9
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I am third party reviewer for this one. I was wondering the same take it to steel. But drawings i got said take it to ground rods so I am wondering if taking to grouns rod splice their woulde be nec 2014 compliant.
    Sent from my SM-G935U using Tapatalk
  10. #10
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Just curious how so GEC size change if brining anothwr set of service conductors? Any article NEC 2014.
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts