    Safety Switches

    Hi,

    I generally deal with just residential PV design, but I'm beginning to tread into commercial design these days. I am dealing with a 3-phase, 208Y/120VAC system, and I am in the process of spec'ing my AC disconnect. I notice there are many 3-pole AC disconnects rated 240/120VAC, and some rated 600VAC. Would the 240/120VAC be suitable for a 208Y/120VAC system?

    Regards,
    Andy

  2. #2
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,424
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by andrew.tkelly View Post
    Hi,

    I generally deal with just residential PV design, but I'm beginning to tread into commercial design these days. I am dealing with a 3-phase, 208Y/120VAC system, and I am in the process of spec'ing my AC disconnect. I notice there are many 3-pole AC disconnects rated 240/120VAC, and some rated 600VAC. Would the 240/120VAC be suitable for a 208Y/120VAC system?

    Regards,
    Andy

    Yes. The 240V disconnects are rated for any circuit that is 240Vac nominal or less between any possible pair of conductors within it.