Results 1 to 3 of 3

Thread: Light fixture mounting

  1. #1
    Join Date
    Dec 2017
    Location
    springfield mo
    Posts
    1

    Light fixture mounting

    Is there a code that says that you need a 8/32 screw minimum size for mounting fixture, 50 pound rated box?

  2. #2
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,330
    Not exactly worded that way but, read 314.27(A)(1) and (2), the listing is the key.

    Roger
    Moderator

  3. #3
    Join Date
    Jun 2005
    Location
    Logan, Utah
    Posts
    8,201
    UL 514A for metallic outlet boxes and UL 514C for nonmetallic outlet boxes both require a minimum of 2 8-32 for supporting a ceiling mounted luminaire of up to 50 pounds.