Results 1 to 8 of 8
Thread: SLC circuit
  1. #1
    Join Date
    Sep 2012
    NJ
    Posts
    1,796
    SLC circuit
    Is an slc the same as an initiating[IDC] circuit? Thanks
    Sent from my SM-G955U using Tapatalk
  2. #2
    Join Date
    Mar 2003
    Massachusetts
    Posts
    93
    No, the SLC is the initiating circuit in an addressable system.
  3. #3
    Join Date
    Sep 2012
    NJ
    Posts
    1,796
    Quote Originally Posted by kelley View Post
    Isn't that what I said/asked?
  4. #4
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,045
    Quote Originally Posted by mstrlucky74 View Post
    The Signal Line Circuit (SLC) carries the power and data for addressable alarm causing devices on an addressable panel (Notifier 9600, for example). The Indicating Device Circuit (IDC) carries the power and signal for conventional (shorting) alarm causing devices on a conventional panel (Silent Knight 5208, for example).
  5. #5
    Join Date
    Sep 2012
    NJ
    Posts
    1,796
    Quote Originally Posted by gadfly56 View Post
    So initiating devices on an addressable system would be on an SLC?
  6. #6
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,045
    Correct.
  7. #7
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    2,403
    FYI, these are terms used in NFPA 72. Proprietary systems may use a different term, but that just makes for confusion. Particularly, Simplex (now Johnson Controls) calls their old system MapNet and the new system IDNet. Both are SLC's
    I know what I don't know, and I know where to go to find it!
  8. #8
    Join Date
    Jan 2016
    Arizona, United States
    Posts
    7
    They are the same in that the are connected to the same types of devices (initiating). They work differently though. Conventional fire alarm systems use IDC circuits/zones, mainly now used for sprinkler monitoring systems. You can put one type of device on each IDC/zone. For example, only smoke detectors on one zone, pull stations on another, water flow's on the next, etc. It works like on/off or open/closed circuit. SLC has power and data in the one circuit and are used in much larger systems. You can mix smoke detectors, pull stations, etc on this same circuit. Each device has it's own address as well to make it easier to identify.