Page 2 of 2 FirstFirst 12
Results 11 to 13 of 13
Thread: Transformer grounding
  1. #11
    Join Date
    Feb 2003
    Illinois
    Posts
    23,623
    Quote Originally Posted by infinity View Post
    If it's not an electrode then no sense connecting to it. Also under the 2017 you need a terminal bar connected to the case of the XFMR.
    What about the requirement in 250.104(D)?
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  2. #12
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,350
    Quote Originally Posted by don_resqcapt19 View Post
    Wouldn't that steel that isn't an electrode already be bonded to the building GES? If so 250.104(D)(2)Exception would already have that covered.
    Rob
  3. #13
    Join Date
    Feb 2003
    Illinois
    Posts
    23,623
    The way I read it, the SDS requires its own bond to the building steel.