User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 15
Thread: Cell tower grounding
  1. #1
    Join Date
    Jul 2013
    Chicago,IL USA
    Posts
    57
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    My company does a lot of cell sites. Grounding scheme is typical on every site- we install a #2 solid ground ring that encircles our equipment platform. All equipment cabinets, h-frames, fence posts, etc are bonded to the ring. The intent of this ring electrode system seems to be to provide a path for a lightning strike.
    Would it be appropriate to view this ring as a service grounding electrode?
    When we install a new service at a site, I view the ring as a seperate GES and provide 2 ground rods for my service GE and bond them to the ring.
    Is this overkill?
  2. #2
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,880
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    We always tied onto the ground ring, never had a problem with an inspector wanting a ground rod and those rods are doing absolutely nothing.
    If you don't think too good, don't think too much.
  3. #3
    Join Date
    Jul 2013
    Chicago,IL USA
    Posts
    57
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    Yeah, I have to agree with your point on the ground rods. Theyre not really achieving anything that the ground ring hasn't already taken care of.
    I suppose the fact that the ring is intended to direct a lightning strike into the earth and away from the equipment doesn't really qualify it as its own seperate 250.106 lightning protection system.
    The fact that 99.9% of our construction drawings always call for a seperate, ( illegally unbonded) isolated ground rod for our service equipment got me wondering if they were viewing the ring as some sort of LPS.
  4. #4
    Join Date
    Feb 2009
    Posts
    9,880
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rojay View Post
    ..The fact that 99.9% of our construction drawings always call for a seperate, ( illegally unbonded) isolated ground rod for our service equipment got me wondering if they were viewing the ring as some sort of LPS.
    That's weird. Not only is it a code violation I have never seen that on a cell site drawing. Who's the carrier if I may be so bold as to ask?
  5. #5
    Join Date
    Feb 2005
    South of Bawstin
    Posts
    1,259
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    From my research on this...the perimeter ground-ring protects the structure and is typically placed at 30-inches below finished grade. The ring at 30-inches may not be below the frost line or the permanent moisture level in some parts of the country, or it may not be deep enough for a low-impedance connection to earth depending on the soil resistivity. The added ground rods that are connected to the ring get deeper into the earth for a better low-impedance path for the lightning to dissipate.
    The ground rods do achieve something more with regard to lightning protection. Sometimes rods are driven deep (40-60feet) into the earth until a satisfactory low resistance-to-earth is established acceptable to the designing engineer.
    This is all over and above what the NEC requires for the Grounding Electrode System. The ground-ring alone qualifies as an electrode with no need for adding rod electrodes.
  6. #6
    Join Date
    Jul 2013
    Chicago,IL USA
    Posts
    57
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Rhymes with C- Noble.
  7. #7
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    8,031
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    By not bonding the separate ground rods to your cell tower ground, there will be difference of potential between the two systems and creates a path into your equipment. The NEC recognizes this and several code cycles ago added intersystem bonding requirements
    Please review NEC definition on Intersystem Bond and rules in 250.94 (A)
    View your cell tower ground as the intersystem bond, 250.94
    Here is a link to Motorola R-56 I consider this the gold standard for telecom grounding
    https://sites.auburn.edu/admin/facil...005_manual.pdf
    Moderator-Washington State
    Ancora Imparo
  8. #8
    Join Date
    Feb 2009
    Posts
    9,880
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Noble just started serving my area. I've hooked up a couple generators for them. I've mostly been involved with Horizon and DDT. I thought all of them would just go with the Motorola R66 spec.
    My hat's off to you if you do the grounding. We never do because the contractor we work for has his own crew just for that. More cad welds going off than the 4th of July when those guys are working.
  9. #9
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,103
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    And if the ground ring is tied to the tower footer you are not going to get any better electrode that the tower concrete footer.
    Brian John
    Leesburg, VA
  10. #10
    Join Date
    Feb 2013
    India
    Posts
    2,551
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by brian john View Post
    Whether it is footer or rod, it helps in easier dissipation of lightning current in association with the earth ring.
Posting Permissions
  • You may not post replies
  • You may not edit your posts