Thread: GEC bonding to enclosure

  1. #1
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,907

    GEC bonding to enclosure

    When a GEC, water bond, ect enters an enclosure, is it required to be bonded at the point of entry?
    I'm in over my head...

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,995
    Is it in a ferrous raceway?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,907
    No
    I'm in over my head...

  4. #4
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,716
    Quote Originally Posted by mbrooke View Post
    When a GEC, water bond, ect enters an enclosure, is it required to be bonded at the point of entry?
    What exactly is this "enclosure" you speak of? 250.64(E)(1) requires it, however I am not sure the intent is to require bonding the a cabinet as it enters. I think there was another thread on this very recently.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  5. #5
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,422
    A common scenario is a GEC that enters a panelboard or meter can via the 1/4" hole supplied by the manufacturer. The GEC is bare, or it is enclosed in PVC and the PVC is butted up to the meter can without a connector. This is an extremely common installation in my area, one I have done myself many times. Some say a free air GEC must be bonded to the enclosure via a "kenny clamp" device. I say no such rule or requirement exists.

  6. #6
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,324
    Quote Originally Posted by mbrooke View Post
    When a GEC, water bond, ect enters an enclosure, is it required to be bonded at the point of entry?
    Forgetting what we think the NEC requires tell us why based on your engineering skills there may be a choke on a GEC through the bottom of an enclosure (maybe an 1/8") and the actual choke (or maybe Lenz law effect) of the same GEC through a ferrous metal "tube".

    Roger
    Moderator

  7. #7
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,907
    Quote Originally Posted by electrofelon View Post
    What exactly is this "enclosure" you speak of? 250.64(E)(1) requires it, however I am not sure the intent is to require bonding the a cabinet as it enters. I think there was another thread on this very recently.
    Meter can, main disconnect, electrical load center- the usual.
    I'm in over my head...

  8. #8
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,716
    Quote Originally Posted by mbrooke View Post
    Meter can, main disconnect, electrical load center- the usual.
    I take the enclosure in 250.64(E) to be a enclosure specifically for the GEC, not a more general enclosure like a cabinet, meter can, etc.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  9. #9
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,907
    Quote Originally Posted by electrofelon View Post
    I take the enclosure in 250.64(E) to be a enclosure specifically for the GEC, not a more general enclosure like a cabinet, meter can, etc.
    Not just the GEC- but all other parts. Breakers, jaws, ect.
    I'm in over my head...

  10. #10
    Join Date
    Nov 2017
    Location
    Oregon City, OR
    Posts
    12

    NOPE

    No matter the enclosure, if there are no splices in the box the GEC can pass through. It can be simply a pull point. Just my experience