    Using EGC as GEC for SDS

    So Can I have a single conductor serve both purposes, if it meets the installation requirements for both? I know this has come up before. It seems the general consensus was there is nothing that prohibits this, however these were all old threads I found and there was mention that there would be language in 2011 prohibiting this. I looked but cant find anything. Just looking for an update, if any.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #2
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    1,257
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    2014 NEC added 250.121 exception that may permit what you are describing.

  3. #3
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,932
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shortcircuit2 View Post
    2014 NEC added 250.121 exception that may permit what you are describing.
    ahhh there it is, thanks.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"