Thread: Using EGC as GEC for SDS

  1. #1
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    3,533

    Using EGC as GEC for SDS

    So Can I have a single conductor serve both purposes, if it meets the installation requirements for both? I know this has come up before. It seems the general consensus was there is nothing that prohibits this, however these were all old threads I found and there was mention that there would be language in 2011 prohibiting this. I looked but cant find anything. Just looking for an update, if any.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #2
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    1,149
    2014 NEC added 250.121 exception that may permit what you are describing.

  3. #3
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    3,533
    Quote Originally Posted by shortcircuit2 View Post
    2014 NEC added 250.121 exception that may permit what you are describing.
    ahhh there it is, thanks.