    FA Device Conduit

    Say you have either a speaker/strobe or strobe mounted recessed in a wall and about 1-2' below drop ceiling? Is it code to have the 1-2' vertical portion in conduit? Thanks

  2. #2
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,225
    Only if local codes require it, there is no NEC rule that does.

  3. #3
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    323
    Quote Originally Posted by mstrlucky74 View Post
    Say you have either a speaker/strobe or strobe mounted recessed in a wall and about 1-2' below drop ceiling? Is it code to have the 1-2' vertical portion in conduit? Thanks
    More information. High rise? Auditorium? Plenum?

  4. #4
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    323
    Sprinkled? Type of construction?

  5. #5
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    5,517
    Quote Originally Posted by mstrlucky74 View Post
    Say you have either a speaker/strobe or strobe mounted recessed in a wall and about 1-2' below drop ceiling? Is it code to have the 1-2' vertical portion in conduit? Thanks
    You may, if you wish, but as others have noted, not required. Check the specifications, drawings and any local regulations for this requirement. I can't imagine anyone prohibiting it, but one or more may require it.