GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Possibly because the sort of things regularly plugged in in bathrooms (e.g. hair dryers) tend to produce unacceptable false trip levels in AFCIs at the time the rule was last rewritten.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I use to think that almost all 120v circuits needed afci in dwellings but I see the bathrooms are exempt. What was the reason that afci was not required in bathrooms but everywhere else?? seems like they wanted to do the whole house to me.
No idea why they left some circuits off the list in the 2014 code, but it appears they have expanded it again for the 2017. The following is from a report on the "first draft" of the 2017 NEC.
210.12(A) - Whole-House AFCI Protection
The continual expansion for arc-fault circuit interrupter (AFCI) protection appears to be complete with the proposed revisions to 210.12(A).
Requires AFCI protection for all 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling units.
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
I use to think that almost all 120v circuits needed afci in dwellings but I see the bathrooms are exempt. What was the reason that afci was not required in bathrooms but everywhere else?? seems like they wanted to do the whole house to me.

You were correct before and you're still correct. Almost all 120v circuits need afci in dwellings.
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
Serious answer:

Before 2008 the requirements were afci in bedrooms. Places you'd be asleep in the event of an arc-fault situation. Makes sense.

Then they realized that people often sleep in the living room, den, or other similar areas. OK...still makes sense.

Then the realization that kitchens were often directly attached to dining rooms and living rooms with no walls between.

The bathroom is the last place that is absolutely closed off from the rest of the house with walls and doors and you are very highly unlikely to be sleeping in there. Unless you have a drinking or drug problem.

But don't worry...Bathrooms will need AFCI soon enough. Then it will be AFCI and dual-function breakers galore! Think of the markup on all the new circuits you sell. It will be glorious. We'll all get rich.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Serious answer:

Before 2008 the requirements were afci in bedrooms. Places you'd be asleep in the event of an arc-fault situation. Makes sense.

Then they realized that people often sleep in the living room, den, or other similar areas. OK...still makes sense.

Then the realization that kitchens were often directly attached to dining rooms and living rooms with no walls between.

The bathroom is the last place that is absolutely closed off from the rest of the house with walls and doors and you are very highly unlikely to be sleeping in there. Unless you have a drinking or drug problem.

But don't worry...Bathrooms will need AFCI soon enough. Then it will be AFCI and dual-function breakers galore! Think of the markup on all the new circuits you sell. It will be glorious. We'll all get rich.

In a perfect world. Unfortunately when harry the home owner bids and finds the sparkie's price is 8 times the handyman special... its safe to guess who gets the job.
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
Yeah, it would be nice if it was an AFCI main because for the most part it would never trip (according to the manufacturer).

I suppose troubleshooting would involve turning off breakers one by one until the main held. But arc-faults don't tend to be a constant tripper.

For instance, today I livened up a circuit that tripped immediately. I went to the area of the circuit and turned off all the switches. Found the switch that was the problem.

Dead shorts are easy to find. Arc-faults are not that easy to find.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Yeah, it would be nice if it was an AFCI main because for the most part it would never trip (according to the manufacturer).

I suppose troubleshooting would involve turning off breakers one by one until the main held. But arc-faults don't tend to be a constant tripper.

For instance, today I livened up a circuit that tripped immediately. I went to the area of the circuit and turned off all the switches. Found the switch that was the problem.

Dead shorts are easy to find. Arc-faults are not that easy to find.

Especially when coming from brand new UL listed appliances.
 

peter d

Senior Member
Location
New England
I certainly hope that resistance to AFCI's gains momentum in the next few years so that more states will amend the AFCI rules out of the NEC.
 

abrace

Member
Location
New Hampshire
Occupation
Telecommunications Engineering
Serious answer:

But don't worry...Bathrooms will need AFCI soon enough. Then it will be AFCI and dual-function breakers galore! Think of the markup on all the new circuits you sell. It will be glorious. We'll all get rich.

Going to have to start using panelboards versus loadcenters in dwelling units. No room left to run the wire with all these AFCI breakers now. Would be nice if they could shrink them down a bit.

It is ridiculously tight in the Square D QO panels as it is.

---Aaron
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
Going to have to start using panelboards versus loadcenters in dwelling units. No room left to run the wire with all these AFCI breakers now. Would be nice if they could shrink them down a bit.

It is ridiculously tight in the Square D QO panels as it is.

---Aaron

Square D is the worst. At least Murray/Siemens and Eaton/Cutler-Hammer are the same sized breakers as the non-afci type. Just a matter of an extra pigtail for the neutral.
 

abrace

Member
Location
New Hampshire
Occupation
Telecommunications Engineering
Square D is the worst. At least Murray/Siemens and Eaton/Cutler-Hammer are the same sized breakers as the non-afci type. Just a matter of an extra pigtail for the neutral.

I have been growing quite fond of Siemens panels. Murray, well, one pitted aluminum bus was all I needed there.

---Aaron
 