    Listed connector for bare copper #6 awg

    Is there a connector available that is listed for bare copper #6 and/or #4 awg grounding wire? We've used 1/2" black plastic button connectors in the past, but they only list Romex in the spec sheets. It would be used for the water pipe ground coming into the panel.

    Sent from my SM-G930P using Tapatalk

  2. #2
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    13,243
    Yes, there is a listed connector. It is called a “kenny clamp”.

    But there is no code section that says you have to use a connector at all.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    16,819
    As Derek points out, a connector is not required by the NEC.

    Roger
    Moderator

  4. #4
    Join Date
    Dec 2013
    Location
    Weymouth, MA USA
    Posts
    6
    Wow!! Thank you!! That was bugging me, haha


    Sent from my SM-G930P using Tapatalk

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    24,177
    Other companies besides Kenny make fittings for this purpose. Bridgeport makes some nice ones too:



    http://www.bptfittings.com/Home/Prod...00781747944450
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted