    Quote Originally Posted by mbrooke View Post
    I honestly do not know

    Though I doubt I will exceed 10,000amps.
    Current limiting fuses are often used to reduce risk of transformer rupture for faults closer to the substation.

    I have never used them on outdoor MV for arc flash reduction but I suppose you could if you found a benefit.
    BB+/BB=?

  2. #42
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,940
    Quote Originally Posted by mivey View Post
    None that I know of but I think about it with lightly loaded transformers and higher voltages.
    At what voltage does it become a concern?
    I'm in over my head...

  3. #43
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,940
    Quote Originally Posted by mivey View Post
    Current limiting fuses are often used to reduce risk of transformer rupture for faults closer to the substation.

    I have never used them on outdoor MV for arc flash reduction but I suppose you could if you found a benefit.
    Seen some POCOs add CLF on pole pigs near the sub- that would make sense.
    I'm in over my head...

  4. #44
    Join Date
    Jan 2008
    Posts
    9,144
    Quote Originally Posted by mbrooke View Post
    At what voltage does it become a concern?
    I don't really worry about systems below at 12 kV and below although it is possible.
    BB+/BB=?

  5. #45
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,940
    Quote Originally Posted by mivey View Post
    I don't really worry about systems below at 12 kV and below although it is possible.
    What would you say about 25kv or maybe even 34.5kv? Also can a modified saturation curve prevent it?
    I'm in over my head...

  6. #46
    Join Date
    Jan 2008
    Posts
    9,144
    Quote Originally Posted by mbrooke View Post
    Seen some POCOs add CLF on pole pigs near the sub- that would make sense.
    The smaller the transformer the greater the risk but usually starting around 4kA to 6kA of fault can be a concern target.
    BB+/BB=?

  7. #47
    Join Date
    Jan 2008
    Posts
    9,144
    Quote Originally Posted by mbrooke View Post
    What would you say about 25kv or maybe even 34.5kv? Also can a modified saturation curve prevent it?
    I would check for favorable conditions, especially on a 34.5kV system.

    Don't know about the sat curve, would have to check.
    BB+/BB=?

  8. #48
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,940
    Quote Originally Posted by mivey View Post
    The smaller the transformer the greater the risk but usually starting around 4kA to 6kA of fault can be a concern target.
    Did not know this- much thanks. Up to 10ka I will just spec a K or T link... I never gave this much thought.

    Quote Originally Posted by mivey View Post
    I would check for favorable conditions, especially on a 34.5kV system.

    Don't know about the sat curve, would have to check.

    Thanks
    I'm in over my head...