    LED- Remote

    If you have duct detectors above hung ceilings where are the remote LED usually mounted? In ceiling? In wall? What wiring used between the duct detector and LED? 2 pair fa cable? Thanks.
    Attached Images Attached Images  

  2. #2
    Join Date
    Aug 2009
    Location
    Cypress, CA
    Posts
    53
    Quote Originally Posted by mstrlucky74 View Post
    If you have duct detectors above hung ceilings where are the remote LED usually mounted? In ceiling? In wall? What wiring used between the duct detector and LED? 2 pair fa cable? Thanks.
    Usually on the ceiling below the duct smoke. I've seen them on walls and columns as well. Mostly a preference.

    Run 1 pair of 2#18 between, FPL or FPLP depending on your ceiling.

  3. #3
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,908
    Quote Originally Posted by ryant35 View Post
    Usually on the ceiling below the duct smoke. I've seen them on walls and columns as well. Mostly a preference.

    Run 1 pair of 2#18 between, FPL or FPLP depending on your ceiling.
    Thanks