    Quote Originally Posted by infinity View Post
    Never mind
    You can, but it is a single shot scenario for getting kVA here.

    We know that 208 x 1.732 = 360 and 120 x 3 = 360, so 90 x 120 is the same as 30 x 208 x 1.732 or (360) works because we know the variables.

    But later with any 208V loads it does not. Cannot just continue add amps.

    It is a limited method that can easily lead to future errors, so I prefer not to even present to people just learning.

    OP keeps getting confused and uses that number thinking he needs a 100A panel like his supply guy.

    It is simply bad methodology to present it to noobs IMO.
    Last edited by infinity; 01-05-18 at 06:54 PM. Reason: Removed confusion
    "Electricity is really just organized lightning." George Carlin


    Derek

  2. #22
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,366
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    You can, but it is a single shot scenario for getting kVA here.

    We know that 208 x 1.732 = 360 and 120 x 3 = 360, so 90 x 120 is the same as 30 x 208 x 1.732 or (360) works because we know the variables.

    But later with any 208V loads it does not. Cannot just continue add amps.

    It is a limited method that can easily lead to future errors, so I prefer not to even present to people just learning.

    OP keeps getting confused and uses that number thinking he needs a 100A panel like his supply guy.

    It is simply bad methodology to present it to noobs IMO.
    After thinking about it I'll just leave it alone.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #23
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    One last thing to add: the 60A panel must be 3ph. If it were 1 phase, supplied by just 2 of 3 legs of a 208V 3ph system, the voltage would be 208V, but the amperage would be ~56A vs ~32A. And tho most know this as well, I'll write it out for the OP: because you have 1ph 120V loads, you will need a grounded (neutral) conductor to your panel in addition to three ungrounded (hot) phase conductors, and a grounding conductor as well if metal raceway isnt used.
    Electricians do it until it Hertz!

  4. #24
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    One last thing to add: the 60A panel must be 3ph. If it were 1 phase, supplied by just 2 of 3 legs of a 208V 3ph system, the voltage would be 208V, but the amperage would be ~56A vs ~32A. And tho most know this as well, I'll write it out for the OP: because you have 1ph 120V loads, you will need a grounded (neutral) conductor to your panel in addition to three ungrounded (hot) phase conductors, and a grounding conductor as well if metal raceway isnt used.
    "Electricity is really just organized lightning." George Carlin


    Derek

  5. #25
    Join Date
    Oct 2016
    Location
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    JFletcher

    You have brought this back to original post...was it not stated his UL listing will be violated if he changes to 3-phase.
    Don't intend on swinging discussion at UL...but if unknown I say keep it 120/208v single phase and don't risk it.
    We know this will be a load center just behind a sliding door. Not a fan, don't like placing an EC on the floor with his/her face in a panel.
    You could probably use #10's and feed all cct's through same conduit the feeder was going in....NO panel needed.

    Tell customers engineer 120/208V-1P (UL issue, can't be changed to 3 phase), load on panel, size of panel lugs and let him decide what to feed with.
    You are building this in your shop....you know the CBer's need to be GFCI ? Yes ?

  6. #26
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MyCleveland View Post
    JFletcher

    You have brought this back to original post...was it not stated his UL listing will be violated if he changes to 3-phase.
    Don't intend on swinging discussion at UL...but if unknown I say keep it 120/208v single phase and don't risk it.
    We know this will be a load center just behind a sliding door. Not a fan, don't like placing an EC on the floor with his/her face in a panel.
    You could probably use #10's and feed all cct's through same conduit the feeder was going in....NO panel needed.

    Tell customers engineer 120/208V-1P (UL issue, can't be changed to 3 phase), load on panel, size of panel lugs and let him decide what to feed with.
    You are building this in your shop....you know the CBer's need to be GFCI ? Yes ?
    My understanding is he is not modifying a 1ph panel to be 3ph, but rather using an off-the-shelf 3ph panel vs the 1ph originally planned:

    "My main question is in sizing the panel (biding the right panel), when converting to amps as per normal the total is 97.1 amps @ 120v this was originally a 125amp single phase panel that the engineer now wants to change to a 3 phase 60amp panel."

    If for some reason he has to stick with the 125A panel originally planned, he can still use it, noting my math in previous posts. 125A 1ph panel either 208V or 240V is more than adequate, it's overkill.
    Electricians do it until it Hertz!

  7. #27
    Join Date
    Oct 2016
    Location
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    My understanding is he is not modifying a 1ph panel to be 3ph, but rather using an off-the-shelf 3ph panel vs the 1ph originally planned:

    "My main question is in sizing the panel (biding the right panel), when converting to amps as per normal the total is 97.1 amps @ 120v this was originally a 125amp single phase panel that the engineer now wants to change to a 3 phase 60amp panel."

    If for some reason he has to stick with the 125A panel originally planned, he can still use it, noting my math in previous posts. 125A 1ph panel either 208V or 240V is more than adequate, it's overkill.
    I see your concerns on correct sizing, but if changing entire design to 3P violates UL then discussion was not helpful.
    Price of a 125mlo 1P vs 3P load center a real concern.

    Something is telling me this is a build from a UL approved design and modification change direction should be coming from the internal factory engineer or designer, not from the guys building it on the plant floor.

  8. #28
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    As far as UL goes, rereading OP, it almost seems that the listing is just for the counter top, receptacles, and kitchen equipment as an assembled package.

    The guy seems to be just trying to spec a minimum supply. Since it is all 120V, a variety of options are available. Not sure if type of supply would be part of listing other than it would have to be adequate.

    120/240V
    120/208V
    208Y/120V

    All three work if sized correctly.
    "Electricity is really just organized lightning." George Carlin


    Derek

  9. #29
    Join Date
    Oct 2016
    Location
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    As far as UL goes, rereading OP, it almost seems that the listing is just for the counter top, receptacles, and kitchen equipment as an assembled package.

    The guy seems to be just trying to spec a minimum supply. Since it is all 120V, a variety of options are available. Not sure if type of supply would be part of listing other than it would have to be adequate.

    120/240V
    120/208V
    208Y/120V

    All three work if sized correctly.
    Agree completely, but wouldn't a factory have a set of options already built-in with the factory designs. This is more a question for the folks who generate the Build Sheets...Yes ?

  10. #30
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MyCleveland View Post
    Agree completely, but wouldn't a factory have a set of options already built-in with the factory designs. This is more a question for the folks who generate the Build Sheets...Yes ?
    Prolly.

    I am waiting for OP to come back so we can explain that most if not all his loads are not continuous per the NEC.
    "Electricity is really just organized lightning." George Carlin