User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 16
Thread: Equipment grounding
  1. #1
    Join Date
    Jan 2018
    Arkansas
    Posts
    4
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Equipment grounding
    Yellow all I have a question about grounding .the other day I ran wire to a 240v 3 phase 4 wire panel . And noticed that there was no grounding bar . Just the neutral bar . Should there not be a grounding bar for equipment grounding
  2. #2
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,044
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Were there wire type egc's in that panel?. It's not unheard of to not have any wire egc's nor a ground bar if it's all metal conduit and the conduot system is the egc
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  3. #3
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Yep, works fine until someone runs say a piece of MC cable to the panel and instead of adding a ground bus sticks the EGC into the neutral bus. See that a lot.
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #4
    Join Date
    Jun 2004
    Posts
    5,044
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    Oh yeah.
  5. #5
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    1,704
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Jay2685 View Post
    ... 240v 3 phase 4 wire panel . And noticed that there was no grounding bar ...
    So the incoming EGC was just landed to the enclosure?
    But yeah, if all metallic conduit suitable for grounding, no wires would be needed...
  6. #6
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,880
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I work in several old buildings that are all conduit and there are no green wires or equipment ground busses in the panels since everything is equipment grounded by the conduit.
    If you don't think too good, don't think too much.
  7. #7
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,048
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Not a problem if the panel is the main service & the neutral is bonded to the can.
    If you aim at nothing, you will hit it every time!
  8. #8
    Join Date
    Jan 2018
    Arkansas
    Posts
    4
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes the electrical sys is all metal conduit.
  9. #9
    Join Date
    Mar 2003
    Vermont
    Posts
    1,953
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I'm interested in if 250.130(C)(4) would apply here>
    (4) An equipment grounding conductor that is part of
    another branch circuit that originates from the enclosure
    where the branch circuit for the receptacle or branch
    circuit originates
    I'm unsure if this is exclusively for extensions of , or new branch circuits originating from a older non-grounding OCPD enclosure
    Perhaps I'm grasping code straws , but let's say one did pick up a EGC from another source
    If it was make back to said enclosure , would it not have to serve the largest OCPD?
    ~RJ~
  10. #10
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,624
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Metallic conduit and tubing is a listed EGC in 250.118 so no wire type EGC's are required. Back 30 years ago we never installed a wire type EGC in a solid metal raceway, it was considered a waste of money. It was common to see no green conductors or EGC bar in a panel.
    Rob
Posting Permissions
  • You may not post replies
  • You may not edit your posts