    Quote Originally Posted by jumper View Post
    Yeah and it was too much for even me to comment on and I got pretty low standards.
    Just wait till someone wonders whether AFCI is needed for the circuit and it’s all over.
    I am gonna go and see if I can find me a 208V high leg delta service to play with.....
    I seen it and commented on it.... just as well hold electrical class on this one..
    JAP>
  2. #122
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Agreed, if the nameplate said one thing and the instructions another, nameplate rules without a doubt.
    This whole thread started because there was no nameplate. Or later OP found it but had not said at beginning. Or was it that some info missing on the nameplate........
    IDK, thread has gotten so muddled I have forgotten at this point.
    There is no nameplate. The drawings aee at design stage not yet permitted. There never was nameplate. Everything coming from engineering drawing which has not yet permitted.
    Heck I dont know how nameplate got involved.
    Sent from my SM-G935U using Tapatalk
  3. #123
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,962
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by codequestion View Post
    I have no idea, my brain is fried on this one.
    I gotta go, there is a large Starbucks double shot of espresso Vanilla flavored Iced Coffee calling my name and I need to answer......
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #124
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,922
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I heard those are best when made on a Starbucks exclusive west coast 208V high leg espresso machine. Enjoy
    If you don't think too good, don't think too much.
  5. #125
    Join Date
    Feb 2009
    Posts
    9,922
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Nameplate became part of the discussion when manufacturer recommendation vs. manufacturer/code requirement entered in.
  6. #126
    Join Date
    Jan 2009
    Posts
    15,962
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    Yeppers.
    Derek
  7. #127
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yeppers.
    Well follow up contacted the engineer who said whats wrong with 25amos it is sized per nec? I said contwct manufacturer and see what the mocp is and 25 amps maybe oversized.
    He said in his 30 years of working as engineer no one has asked him to do.
  8. #128
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,452
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I suppose he can put whatever he wants as long as the conductors supplying the unit are sized properly. Also assuming that the manufacturer hasn't specified a max size for the OCPD. Which he should check. Not your job.
  9. #129
    Join Date
    Nov 2009
    Opelousas, Louisiana
    Posts
    597
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You could run a 25 amp circuit to a disconnect and then fuse the disconnect at 15 amps. If this is a commercial job, at least the engineers I deal with, always spec a fused disconnect at the unit.
  10. #130
    Join Date
    Jan 2007
    Posts
    3,947
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Mgraw View Post
    Per post #73 the OP stated the engineer has drawn a 25 amp circuit to a 20a NF Disconnect.
    I don't see how this could be since actual NF disconnects start a 30 amps.
    Generally an engineer will draw a disconnect symbol on the prints and if it has a (20) beside it that means it should be a 30 amp fused disconnect fused at 20amps.
    If this is actually the case, then the OP misread the print, since even it were indicated to be fused at 20 amps the change to a 15 amp fuse would not result in a price increase and no change order would be needed.
    If this is a bid job and the engineer actually indicated the disconnect to be a "Non Fused" 20a disconnect, then a change order should be submitted to change the "Non Fused" disconnect to a 30 amp "Fused Disconnect" with 15 amp fuses and be done with it.
    JAP>