  1. #1
    Join Date
    May 2013
    Tujunga, CA
    Posts
    449
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Fast Delta Calc
    Hi ,
    Do you think that I can estimate a remodeled warehouse load supplied by the existing 120/240V, 4wire, 3 phase service
    this way ?????????;
    General ltg w/ 25% LCL = 2400VA @ 120/240v, 1 ph. = 10A
    Gen. use recept @ 100= 2400VA= @ 120/240, 1ph= 10A
    special . use recept @ 100= 4800VA= @ 120/240, 1ph= 20A
    miscel. @ 100= 1200VA= @ 120/240, 1ph= 5A
    Motorized load @ 100= 12,450VA @ 415V, 1ph= 30A (some used the high leg)
    roof mtd AC load @ 100= 12,450VA @ 415V, 3ph= 30A
    sub total , 2pole+3 ph loads= 60A
    sub total, 1 ph, grounded loads= 45A
    Largest motor @ 25%= 2075VA @ 415V= 5 A
    120% PF for existing-old motorized loads= (13000 x 1.2= 15,600 / 415V= 38A
    Concluded that;
    minimum service @ 120/240, 3 ph, 4w required is; 148A
    Thank you
  2. #2
    Join Date
    Feb 2003
    Connecticut
    Posts
    3,242
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Toros View Post
    Hi ,
    Concluded that;
    Where is the 415V coming from?
  3. #3
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by david luchini View Post
    One might also wonder abput this:
    "the existing 120/240V, 4wire, 3 phase? service "
  4. #4
    Join Date
    May 2013
    Tujunga, CA
    Posts
    449
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    240v x 1.73=415 v
  5. #5
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    240v x 1.73=415 v
    Sounds like EU voltages. Except for the 120V.
  6. #6
    Join Date
    Jan 2011
    United States
    Posts
    8,332
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by Besoeker View Post
    Its this:
    Delta high leg is great for long runs because standard 208-230 volt motors are unlikely to encounter under voltage issues.
    I'm in over my head...
  7. #7
    Join Date
    Oct 2016
    Cleveland, Ohio
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    mbrooke
    Excellent graphics....can I ask what program was used to generate, or was this all cut and paste ?
  8. #8
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    Its this:
    But no mention of 415V.
  9. #9
    Join Date
    Jan 2011
    United States
    Posts
    8,332
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by MyCleveland View Post
    mbrooke
    They are Mike Holt's. Not sure what program he or his team made them on, but they sure are the best graphics bar none.
    Oppps- missed that But to be fair you do get 415 volts L-N on a 240/480 delta.
  10. #10
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Don't see how but then I'm thick according to one of the mods here.