Thread: Stepping up from 480Y/277V to 12470Y/7200V

  1. #1
    Join Date
    Aug 2010
    Posts
    152

    Stepping up from 480Y/277V to 12470Y/7200V

    I have a project with a campus loop type electrical distribution system. The campus loop is fed from a 15kV Medium Voltage (MV) Switch. The MV Switch can be fed from either the electric utility or a client owned Tier 3 emergency generator. The generator is a 1400KW, 480Y/277V, diesel engine, and the voltage system is stepped up on the emergency side of the MV Switch. The voltage system is stepped up via a 1500KVA transformer from 480Y/277V to 12470Y/7200V.

    The client is part of an Emergency Back-up Generator Program with the utility company, where they get monthly rebates in exchange for the utility company being able to switch the generator on to feed the campus loop when necessary. The utility company is requiring the generator to be replaced from a Tier 3 to a Tier 4 generator in order for the client to stay in the rebate program. The client just wants to replace the generator only, without making any upgrades or system changes. The generator is currently located in a very basic aluminum building shed.

    My question is, it seems impractical to get a new 480Y/277V generator and step up the system voltage to 12470Y/7200V. Is this stepping up a voltage commonly done at the electrical distribution level? What upgrades would need to be done with the system and the building if we did look at going with a 12470Y/7200V generator? What codes besides the NEC and NESC should I be looking to comply with for the Medium Voltage (124700V/7200) generator? What upgrades would need to be made to the basic metallic building shed if we did change to a 12470Y/7200V generator and didn't go with the step-up scenario?

    All help is appreciated.

  2. #2
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    7,173
    A) It's done all the time, because....

    B) The owner of the generator must only deal with the 480V class control / metering / protection / maintenance, the MV step-up transformer and switchgear then becomes a different system falling under a different jurisdiction (whether internal or external).

    If you generate at 12.47kV, ALL of the switchgear / protection / metering etc. is going to cost a WHOLE lot more and the same people who are qualified to work on other 480V systems in your facility can likely no longer work on the generator.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  3. #3
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,530
    a couple of things to check
    genset price: 12470 vs 480
    is the utility going to require a 1:1 iso xfmr or are you allowed direct tie to their grid

    it seems like all your ats, relaying, synchronizing gear is on the 12470 side
    so all you need is the genset



  4. #4
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,388
    It seems very practical just to replace the 480V gen and leave everything else alone. The step up process and protective relating is already there to grid tie, so just replace the gen.

    The Tier 4 emissions will be bigger than the Tier 3 emissions equipment, so the very basic aluminum building shed will become bigger. You will likely want to just buy the generator in an enclosure from the vendor with all the accouterments. Be sure it comes from the vendor Tier 4 fitted out and tested and not modified by a local person as Tier 4 modified so the EPA will not give you a hard time.
    Ron

  5. #5
    Join Date
    Mar 2014
    Location
    South Florida
    Posts
    148
    got a one line you are permitted to share?

  6. #6
    Join Date
    Oct 2013
    Location
    MD
    Posts
    52
    I agree sticking with LV is probably the better route. Note, your transformer is slightly undersized and will limit the generator from providing full output. Almost all generators are rated with 0.8 pf so it has 1750kVA rating. I'm sure your actual load power factor is higher but worth noting and reviewing the tranformer protection. You should be also be able to talk with the generator manufacturer to limit excitation to not overload the transformer.
    If you go the MV route, there are generators available in that voltage though it is at the upper end of available units. Above 13kV, the stator insulation gets too thick that it is not practical. Also an MV generator would not be solidly grounded like the existing LV generator. You would have to use a resistor and/or reactor impedance ground and provide the proper protective relaying. It is more difficult than specifying a mccb but I'm sure the gen mfr can help.
    One thing I've heard on the Tier 4 is that many are specifying the emissions package as a 3rd party piece of equipment. This is so inducement controls are not hard programmed in to the generator ECM. I won't say more than that, I'm sure you can come up with the reason.
    "Emergency Operation—To facilitate the use of certain nonroad engines in temporary emergency situations, the engines can be equipped with an AECD to override performance inducements related to the emission control system—for example, to allow engine operation without urea in the SCR system during an emergency [EPA 2014]. This flexibility is intended primarily for engines used in construction equipment and portable equipment used for temporary power generation and flood control." https://www.dieselnet.com/standards/us/nonroad.php

    Also note the UREA or diesel exhaust fluid DEF consumption rates can be signifigant. You'll likely have to provide a chemcical storage tank and consider a containment area around the tank for the bulk storage necessary. Coordinate tank volume with local delivery service truck volumes and schedule. If it is outside, heat tracing is required as UREA freezes fairly low. Hope that helps - good luck.

  7. #7
    Join Date
    Aug 2010
    Posts
    152
    Quote Originally Posted by drktmplr12 View Post
    got a one line you are permitted to share?
    One-Line As-built of Existing System

    Name:  As-Built.JPG
Views: 121
Size:  113.3 KB

  8. #8
    Join Date
    Oct 2013
    Location
    MD
    Posts
    52
    If it were me I'd consider replacing the 1500kVA generator step up transformer with a 2000kVA wye grounded HV side and delta LV side. Talk to mfr's like Virgina Transformer Corporation, Howard Industries, etc. not the standard distribution transformer mfrs. Would also recommend having the impedance of all these transformers on the drawing as well. I would consider upsizing all of the MV distribution conduits from 4" to 5". Why no ground conductor in MV conduits other than the two main feeds from the main gear?

    Recommend you get a copy of and review:
    T-030 - Cummins Application Eng Guide Chapter 5
    ieee_c57-116_1989-transformers-directly-connected-to-generators
    ANSI-IEEE C37.102-1987 GUIDE FOR AC GENERATOR PROTECTION

  9. #9
    Join Date
    Aug 2010
    Posts
    152
    Quote Originally Posted by smoothops10 View Post
    If it were me I'd consider replacing the 1500kVA generator step up transformer with a 2000kVA wye grounded HV side and delta LV side. Talk to mfr's like Virgina Transformer Corporation, Howard Industries, etc. not the standard distribution transformer mfrs. Would also recommend having the impedance of all these transformers on the drawing as well. I would consider upsizing all of the MV distribution conduits from 4" to 5". Why no ground conductor in MV conduits other than the two main feeds from the main gear?

    Recommend you get a copy of and review:
    T-030 - Cummins Application Eng Guide Chapter 5
    ieee_c57-116_1989-transformers-directly-connected-to-generators
    ANSI-IEEE C37.102-1987 GUIDE FOR AC GENERATOR PROTECTION
    This is an as-built drawing of their current instalaltion. I have not started the design yet.

  10. #10
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,530
    based on the single line
    why the 480 xfer switch since the 12.47 gear has one too?
    the only thing that feeds it is the gen?

    me: get rid of the gen, ats, xfmr and get a 12.46 gen as long as the cost delta is not too large and they do not require a 1:1 iso xfmr