    Help with 215.10 (2014 NEC)

    Hi,
    I'm studying for my C5 Inspection Certificate and am looking for a little clarification. I purchased the Mike Holt study material and came across a question I couldn't answer (and my seasoned colleagues couldn't answer).

    One of the questions asks : Ground-fault protection of equipment shall be required for a feeder disconnect if the disconnect is rated _____

    A)800a/208V
    B)800A/480V
    C)1000A/208V
    D)1000A/480V

    So the answer stated in the Answer Key says the answer is "D" and refers you to section 215.10.
    215.10 states : Each feeder disconnect rated 1000 amperes or more and installed on solidly grounded wye electrical system of more than 150 volts to ground, but not exceeding 600 volts phase to phase, shall be provided with ground fault protection of equipment in accordance with the provisions of 230.95.

    My question is, wouldn't "C" and "D" be correct because they are both above 150V and both smaller than 600V? Am I missing something? Is it impossible for a wye electrical system to be 208v because there are 3 hot legs?

    Any help is greatly appreciated. Thank you all.

  2. #2
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    18,938
    Quote Originally Posted by bisom View Post
    Am I missing something?
    Yes you are, but it is a subtle tidbit. The rule you quoted says "more than 150 volts to ground." A 208V system has 208 volts phase to phase, but only 120 volts to ground.

    Welcome to the forum.

    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    24,958
    (D) is the best answer but for a 480 volt system the answers should indicate that the system is actually a solidly grounded WYE system. The choice of (D) could be a ungrounded system or a 3 wire Delta.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Jul 2012
    Location
    Houston
    Posts
    21
    D. See Charlie B's reply.

  5. #5
    Join Date
    Jan 2018
    Location
    SanDiego
    Posts
    2
    Thank you guys very much. So I guess my follow up question would have to be, Where can I learn why 120v goes to ground on this system? Is it like this on a delta system? Go easy on me, I'm just starting to learn this trade.

  6. #6
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,449
    Quote Originally Posted by bisom View Post
    Thank you guys very much. So I guess my follow up question would have to be, Where can I learn why 120v goes to ground on this system? Is it like this on a delta system? Go easy on me, I'm just starting to learn this trade.
    Here is a post from a great member here who is no longer active. It is an explanation of what you seem to asking. Give it a read.

    http://forums.mikeholt.com/showthrea...650#post708650
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.

  7. #7

    Help with 215.10

    Quote Originally Posted by bisom View Post
    Thank you guys very much. So I guess my follow up question would have to be, Where can I learn why 120v goes to ground on this system? Is it like this on a delta system? Go easy on me, I'm just starting to learn this trade.
    The answer to your follow up question (1) quoted above is illustrated in exhibit 230.27 & exhibit 230.28 (NEC 2014) if you have a hand book to view the exhibits otherwise think of it as where the OCPD is located on the Wye portion of the transformer (delta/wye) and the load conductors including the neutral (previously discussed) where the ground fault sensor is located. In general a 480Y/277V or a 600Y/437V transformer secondary was the caveat for adding distinction to prevent burndown adopted in 1971(according to the source relative to transformer protection in NEC 450-3 answers your other delta-delta question above). This will lead you to other transformer protection not asked in the original post of 215.10 since that is feeder protection and or services protection related to the 230.95 portion of your OP.

  8. #8
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,764
    Quote Originally Posted by bisom View Post
    Thank you guys very much. So I guess my follow up question would have to be, Where can I learn why 120v goes to ground on this system? Is it like this on a delta system? Go easy on me, I'm just starting to learn this trade.
    The 120 volts doesn't "go to ground" as you put it, but it is measured to ground in a system with an intentionally-grounded conductor, mainly because we're concerned with the possible shocking of a person who accidentally contacts an energized point.


    Quote Originally Posted by ActionDave View Post
    Here is a post from a great member here who is no longer active. It is an explanation of what you seem to asking. Give it a read.

    http://forums.mikeholt.com/showthrea...650#post708650

    Why, thank you! Flattery will get you everywhere. I'm back!
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,267
    Quote Originally Posted by bisom View Post
    Hi,
    I'm studying for my C5 Inspection Certificate and am looking for a little clarification. I purchased the Mike Holt study material and came across a question I couldn't answer (and my seasoned colleagues couldn't answer).

    One of the questions asks : Ground-fault protection of equipment shall be required for a feeder disconnect if the disconnect is rated _____

    A)800a/208V
    B)800A/480V
    C)1000A/208V
    D)1000A/480V

    So the answer stated in the Answer Key says the answer is "D" and refers you to section 215.10.
    215.10 states : Each feeder disconnect rated 1000 amperes or more and installed on solidly grounded wye electrical system of more than 150 volts to ground, but not exceeding 600 volts phase to phase, shall be provided with ground fault protection of equipment in accordance with the provisions of 230.95.

    My question is, wouldn't "C" and "D" be correct because they are both above 150V and both smaller than 600V? Am I missing something? Is it impossible for a wye electrical system to be 208v because there are 3 hot legs?

    Any help is greatly appreciated. Thank you all.
    Solidly grounded wye systems will have the neutral point grounded to comply with 250.26. Line to neutral voltage will always be line to line voltage divided by 1.732. This gives you the three most common North American wye systems of 208/120, 480/277 and 600/347.

    120 volts is low enough it doesn't really sustain arcing without feeding more into matter into the arc.

    277 volts is much more common see an arcing situation just continue to arc until things melt down.

    I suppose they just chose to word it as over 150 volts to ground to give slight leeway to exclude 208/120 systems but want to include anything over that.

    600/347 volt systems are more common in Canada but you can find some in US.

    Over 600 volts has traditionally been entirely different set of rules for many aspects, though that is sort of shifting more toward 1000 volts in recent code editions.