Thread: How to size neutral

  1. #1
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    299

    How to size neutral

    I have 120/208v single phase A AND C tapped from three phase 120/208V trough to Panel F. Lanel F A phase has 32.25 amps and C phase has 48.17 amps. What would the neutral size be per nec 210.61?

    Sent from my SM-G935U using Tapatalk

  2. #2
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    13,240
    This article may be helpful as a start:

    http://www.ecmweb.com/code-basics/ch...tral-conductor

    Google has a lot of hits on the subject.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    299
    Quote Originally Posted by jumper View Post
    This article may be helpful as a start:

    http://www.ecmweb.com/code-basics/ch...tral-conductor

    Google has a lot of hits on the subject.
    It is still confusing. I ahve 3 phase 120/20v to trough and from the trough their is a feeder tap to 120/208v single phase panel phase A and C with amps.original poster. Not sure how to size neutral per nec 210.61.

    Sent from my SM-G935U using Tapatalk

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,321
    For that application, the neutral needs to be the same size as the phase conductors. The maximum unbalanced neutral current is the current with only loads on the highest loaded phase. Even with equal loads on the two ungrounded conductors, you will have the same current on the neutral. It does not cancel where you are using only two phases of a 3 phase wye system.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    34,323
    Quote Originally Posted by don_resqcapt19 View Post
    For that application, the neutral needs to be the same size as the phase conductors. The maximum unbalanced neutral current is the current with only loads on the highest loaded phase. Even with equal loads on the two ungrounded conductors, you will have the same current on the neutral. It does not cancel where you are using only two phases of a 3 phase wye system.
    Didn't read code to verify - but logic tells me it should only need to be as large as maximum line to neutral load possibilities. Say you fed an apartment (common place to see 208/120 three wire) and had some electric space heating @ 208 volts, water heating @ 208 volts range (gets a little more complex because many have some 120 volt load), then you have already taken up some of the feeder capacity with loads that will not utilize the neutral. I don't see you needing full capacity neutral in that case but rather one that can handle the maximum possible current that may be imposed on the neutral. Keep in mind if there is extremely limited neutral load the feeder neutral still needs to be at least as large a the required EGC.

  6. #6
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,321
    Quote Originally Posted by kwired View Post
    Didn't read code to verify - but logic tells me it should only need to be as large as maximum line to neutral load possibilities. Say you fed an apartment (common place to see 208/120 three wire) and had some electric space heating @ 208 volts, water heating @ 208 volts range (gets a little more complex because many have some 120 volt load), then you have already taken up some of the feeder capacity with loads that will not utilize the neutral. I don't see you needing full capacity neutral in that case but rather one that can handle the maximum possible current that may be imposed on the neutral. Keep in mind if there is extremely limited neutral load the feeder neutral still needs to be at least as large a the required EGC.
    You are correct...the maximum line to neutral load that is on any of the phase conductors. Thanks for catching that.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    34,323
    Quote Originally Posted by codequestion View Post
    I have 120/208v single phase A AND C tapped from three phase 120/208V trough to Panel F. Lanel F A phase has 32.25 amps and C phase has 48.17 amps. What would the neutral size be per nec 210.61?

    Sent from my SM-G935U using Tapatalk
    There is no 210.61. (at least in 2014 and 2017), you type the wrong section you are questioning?

  8. #8
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    299
    Quote Originally Posted by kwired View Post
    There is no 210.61. (at least in 2014 and 2017), you type the wrong section you are questioning?
    Huh oh its 220.61 NEC 2014

    Sent from my SM-G935U using Tapatalk

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    34,323
    Quote Originally Posted by codequestion View Post
    Huh oh its 220.61 NEC 2014

    Sent from my SM-G935U using Tapatalk
    Just wanted to make sure what section you were asking about - replies so far are in accordance with that section.

    So you have 32.25 on one line and 48.17 on the other. If all the loads are 120 volt then you need at least 48.17 amp neutral conductor.

    If you have some straight 208 volt loads mixed in you can subtract those, they don't impose any current on the neutral.

    You can not have neutral any smaller then the required EGC though. (have to look for where that is but I know it is in there)