    220.61 exception

    220.61 (A) exception says for 3 wire 2 phase. Does this include 120/208V single phase derived from trough 120/208v three phase? It would have 2 phase.

    Sent from my SM-G935U using Tapatalk

  2. #2
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    1,094
    Instead of each one of us grabbing our Code books for all your questions, please take the time to cut-and-paste it into your question. Let's all get on the same page with the exact wording of the exact year Code you are using.

    What does "derived from trough 120/208" mean? Is that another typo? These questions would probably be easier and more accurate to ask if they weren't from your phone.

    What are you calling 2-phase?

  3. #3
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    300
    Quote Originally Posted by MAC702 View Post
    Instead of each one of us grabbing our Code books for all your questions, please take the time to cut-and-paste it into your question. Let's all get on the same page with the exact wording of the exact year Code you are using.

    What does "derived from trough 120/208" mean? Is that another typo? These questions would probably be easier and more accurate to ask if they weren't from your phone.

    What are you calling 2-phase?
    Tapped from trough. The 2 phas 3 wire is wording from nec 2014 text.

    Sent from my SM-G935U using Tapatalk

  4. #4
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    300
    Sorry ignore previous post. Thats the wording coming from nec 2014.



    Sent from my SM-G935U using Tapatalk

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    24,179
    Quote Originally Posted by codequestion View Post
    220.61 (A) exception says for 3 wire 2 phase. Does this include 120/208V single phase derived from trough 120/208v three phase? It would have 2 phase.
    No, that reference is for a 2-phase system not single phase from a 3 phase system.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    300
    Quote Originally Posted by infinity View Post
    No, that reference is for a 2-phase system not single phase from a 3 phase system.
    What are these 2 phase system 120/240v or 120/208v?

    Sent from my SM-G935U using Tapatalk

  7. #7
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,623
    Quote Originally Posted by codequestion View Post
    What are these 2 phase system 120/240v or 120/208v?

    Sent from my SM-G935U using Tapatalk
    A two phase system has at least two phase conductors whose phasors differ by 90 degrees.
    It can be two hot and one "neutral" where L1-N is offset 90 degrees from L2-N.
    Or it could be four wire "square" with no neutral conductor and 90 degree rotations as you go around the square.
    Or it could be a star with four hots and a common neutral.
    Or a couple of other unlikely combinations in between. The common thread is the 90 degree phase rotation.
    The star configuration can be looked at as two crossed three wire single phase 120/240 systems with both neutrals sharing a wire.

  8. #8
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    13,270
    Quote Originally Posted by GoldDigger View Post
    A two phase system has at least two phase conductors whose phasors differ by 90 degrees.
    It can be two hot and one "neutral" where L1-N is offset 90 degrees from L2-N.
    Or it could be four wire "square" with no neutral conductor and 90 degree rotations as you go around the square.
    Or it could be a star with four hots and a common neutral.
    Or a couple of other unlikely combinations in between. The common thread is the 90 degree phase rotation.
    The star configuration can be looked at as two crossed three wire single phase 120/240 systems with both neutrals sharing a wire.
    Nope, I told you all since I have never seen it, do not like it, and is confusing:

    Two phase does not exist.

    It nothing more than a conspiratorial plot to drive me bonkers......
    "Electricity is really just organized lightning." George Carlin


    Derek

  9. #9
    Join Date
    Sep 2008
    Location
    UK
    Posts
    10,563
    Quote Originally Posted by GoldDigger View Post
    A two phase system has at least two phase conductors whose phasors differ by 90 degrees.
    Sott and Le Blanc connections are usually two phase.
    Si hoc legere scis nimium eruditionis habes.

  10. #10
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    13,270
    Quote Originally Posted by Besoeker View Post
    Sott and Le Blanc connections are usually two phase.
    One of these?

    Name:  Scott-T.JPG
Views: 45
Size:  24.9 KB
    "Electricity is really just organized lightning." George Carlin


    Derek