    Can you tag out a light switch to fix a lighting fixture in a room?

  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,285
    Quote Originally Posted by yucatan4 View Post
    Can you tag out a light switch to fix a lighting fixture in a room?
    You can "tag it out", I suppose, but what is missing is the "lock out" part of the Lock Out/Tag Out combination.

    Even if it was in my sight the whole time, I would not feel comfortable working on the fixture unless I could figure out a way to at least lock the switch against casual operation.
    If the work is covered by OSHA, no way!

  3. #3
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    5,837
    Quote Originally Posted by GoldDigger View Post
    You can "tag it out", I suppose, but what is missing is the "lock out" part of the Lock Out/Tag Out combination.

    Even if it was in my sight the whole time, I would not feel comfortable working on the fixture unless I could figure out a way to at least lock the switch against casual operation.
    If the work is covered by OSHA, no way!
    GIYF; see here.

    Click image for larger version. 

Name:	41DzQbtJCUL._SX342_.jpg 
Views:	135 
Size:	24.6 KB 
ID:	19310

  4. #4
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,285
    Quote Originally Posted by gadfly56 View Post
    GIYF; see here.
    Nice. And the locked cover covers the screws that attach it.
    No help for Decora or other odd style switches, and maybe a pain to attach as needed, but it does seem to satisfy the rules and be practical.

  5. #5
    Join Date
    Mar 2016
    Location
    The Motor City, Michigan USA
    Posts
    736
    Turning off the switch does not assure that the wires in the light-fixture box are off. It's likely that one will remain hot.

  6. #6
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,285
    Quote Originally Posted by drcampbell View Post
    Turning off the switch does not assure that the wires in the light-fixture box are off. It's likely that one will remain hot.

    Such as when the switch is on a switch leg from a powered box.

  7. #7
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,201
    Quote Originally Posted by GoldDigger View Post

    Such as when the switch is on a switch leg from a powered box.
    Or a constant hot for an EM fixture. Supposed to be an indicator but stuff happens...

    And fixtures can be raceways at times so....it’s a bit of fun at times opening wiring sections.
    "Electricity is really just organized lightning." George Carlin


    Derek

  8. #8
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,362
    If the toggle switch is within sight how is this any different than a toggle switch being used as a disconnecting means for a piece of equipment?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  9. #9
    Join Date
    Mar 2016
    Location
    The Motor City, Michigan USA
    Posts
    736
    Um, because it doesn't necessarily disconnect? (see above)

  10. #10
    Join Date
    Mar 2005
    Location
    Hampton, VA
    Posts
    348
    Here is an OSHA interpretation letter on the subject.