    I'm having a hard time understanding the requirements when feeding a motor from a jbox,disconnect or vfd to a motor to size the wire.How is tap rule applied?Any help would be appreciated. Thanks
  2. #2
    Join Date
    Oct 2015
    US
    Posts
    789
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    How long is the wire from the point your splicing to the load served?
    Sent from my SM-G950U using Tapatalk
  3. #3
    Join Date
    Oct 2015
    US
    Posts
    789
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    There are more circumstances involved in sizing conductors for motors is it a.
    Branch circut?
    Feeder?
  4. #4
    Join Date
    Feb 2003
    Illinois
    Posts
    23,902
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There are no tap rules involved for a single motor on the load side of the motor branch circuit overcurrent protective devices.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  5. #5
    Join Date
    Jun 2017
    WI, USA
    Posts
    387
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by nickelec View Post
    Branch circut?
    Feeder?
    How would serving a motor be a feeder?
  6. #6
    Join Date
    Oct 2015
    US
    Posts
    789
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    You never seen a feeder feeding an OCPD serving multiple motors?
  7. #7
    Join Date
    Jun 2017
    WI, USA
    Posts
    387
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Mightymite47 View Post
    These are sized the same as the motor circuit conductors.
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Tap rule would be a situation where you "tap" from a feeder and end up in an overcurrent device to protect the branch circuit on the load side of that device.
    Say you ran a 100 amp feeder across the plant to an area where you had a group of motors. Near those motors you maybe place a gutter or splice box and make taps to that 100 amp feeder to several 30 amp fused disconnects each to supply a motor circuit of 30 amps or less.
    Tap rule covers any conductor between the feeder and each overcurrent device that has lesser ampacity then the feeder.
    See 240.21(B)
  9. #9
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,937
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    See 240.21(B)
    More specifically, IMHO, it covers any situation where a conductor (other than a service conductor) is protected at its rated ampacity only at the downstream end rather than at the upstream end.
  10. #10
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    Yes.