    Quote Originally Posted by jumper View Post
    ...wait.. maybe this is OPs confusion....

    Lights like paddle fan and track outside a shower. 410.10(D).

    Switches, certain light fixtures, shower.....Whadda ya think?
    - Totally forgot about that one.

  2. #12
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,595
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    There is no 3' requirement from the tub in any NEC version. The code simply says that it cannot be within shower and tub spaces which means if you draw a vertical line at the edge of the shower or tub it must to the outside of the line.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #13
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    387
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    No requirement for 3 foot.