Thread: Overdutied Equipment Labeling

  1. #11
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,755
    Quote Originally Posted by wbdvt View Post
    As the consultant that finds the overdutied equipment, I always put in the report that it is a violation of NEC and OSHA but my concern is that this information may not get to the workers and they would no way of knowing that the device that are operating may be overdutied and should not be operated energized. But perhaps that is all I can do, highlight it with strong language in the report.
    Just how would they operate it de-energized?

    The thing about SCCR is that there is a ton of stuff out there that has been in place for many decades that is almost certainly on a system that can supply more short circuit current than the equipment is rated for. I have NEVER seen any credible research reports suggesting it has ever actually been a problem. none. Zero. I think it is a potential problem, but the fact that it is not killing people suggests maybe it is overblown as problems go.

    Arc flash related stuff OTOH is a real problem that continues to kill people yet we do almost nothing about it code wise that makes any real difference. At least the Canadians mandated the separation of the main in a PB into a seperate section. Not perfect but an improvement. We just make more rules that are hard to understand and often even harder to follow and then wonder why the problem does not get all that much better. There is a reason why engineering controls are not considered a good first step in safety measures. Engineering controls are a last resort as far as safety measures go but for something as deadly as arc flash injuries that is where we are starting from.
    Bob

  2. #12
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    34,304
    Quote Originally Posted by petersonra View Post
    Just how would they operate it de-energized?

    The thing about SCCR is that there is a ton of stuff out there that has been in place for many decades that is almost certainly on a system that can supply more short circuit current than the equipment is rated for. I have NEVER seen any credible research reports suggesting it has ever actually been a problem. none. Zero. I think it is a potential problem, but the fact that it is not killing people suggests maybe it is overblown as problems go.

    Arc flash related stuff OTOH is a real problem that continues to kill people yet we do almost nothing about it code wise that makes any real difference. At least the Canadians mandated the separation of the main in a PB into a seperate section. Not perfect but an improvement. We just make more rules that are hard to understand and often even harder to follow and then wonder why the problem does not get all that much better. There is a reason why engineering controls are not considered a good first step in safety measures. Engineering controls are a last resort as far as safety measures go but for something as deadly as arc flash injuries that is where we are starting from.
    Having higher available current then equipment rating isn't a problem, until someone closes a switch into a fault, or is standing by that equipment at the right moment when it does have a failure.

    I don't get into many places that have over 1200 amp supply to them, but what I have generally noticed below that level is that you generally are below max available fault current with equipment ratings if you have at least 25 feet maybe occasionally up to 50 feet of conductor between transformer and service equipment. And even if you are over the rating of branch units they usually will be series rated with the service disconnect. That don't mean there isn't going to be high arc flash energy available, just that the equipment is within acceptable ratings.

  3. #13
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    13,234
    Quote Originally Posted by wbdvt View Post
    As the consultant that finds the overdutied equipment, I always put in the report that it is a violation of NEC and OSHA but my concern is that this information may not get to the workers and they would no way of knowing that the device that are operating may be overdutied and should not be operated energized. But perhaps that is all I can do, highlight it with strong language in the report.
    Not an EE or any type of consultant, but I would want confirmation that report was received and a well written statement that the owner read and understands exactly the situation you are addressing.

    Major CYA documentation with signatures.

    I have a real healthy sense of paranoia for stuff like this.
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #14
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    301
    It happens. There should be reasonable evaluation as to why the existing equipment ratings as less than true available. Generally, utility agreements maintain a threshold of allowable increase in available fault current. That would be my first investigation.

    Otherwise, one might take measures to solve this short/long term by having an engineered series rating modifications.

    Otherwise, yes - there is cause for concern. However, it depends on the situation. If this equipment were in an unoccupied vault, for instance, maybe it is reasonable to continue operation for while waiting on lead time needed for replacement. Maybe the same is true for an occupied space, so long as NFPA 70E alerting techniques are followed to avoid technicians operating the equipment. Maybe you’d consider different if it were an industrial facility under single management.

    We have all seen equipment with high enough AIC ratings needed, but the equipment condition itself is questionable - that same equipment continues to be in operation for many years beyond service life should be subject to the same criticisms, but they aren’t always.

    Some due diligence is needed when we find these and the specific solution...depends. In all cases, owners carry high liability and OSHA is waiting in the shadows.

  5. #15
    Join Date
    Dec 2010
    Posts
    1,342
    There is a good discussion of the topic with sample labels here https://brainfiller.com/arcflashforu...hp?f=24&t=4518
    The more they overthink the plumbing, the easier it is to stop up the drain

  6. #16
    Join Date
    Feb 2013
    Location
    India
    Posts
    2,278
    Why not also send a note to OSHA as a responsible electrical professional?

  7. #17
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    34,304
    Quote Originally Posted by Sahib View Post
    Why not also send a note to OSHA as a responsible electrical professional?
    Because your clients hired you to help them comply not to turn them in to be fined. Other alternative for them is to just call OSHA directly and have them come inspect things - then fine you for anything non compliant, that would save paying the middle man (the OP).

  8. #18
    Join Date
    Feb 2013
    Location
    India
    Posts
    2,278
    Quote Originally Posted by kwired View Post
    Because your clients hired you to help them comply not to turn them in to be fined. Other alternative for them is to just call OSHA directly and have them come inspect things - then fine you for anything non compliant, that would save paying the middle man (the OP).
    Either way it should deter the owners to keep an unsafe condition.

  9. #19
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    13,234
    Quote Originally Posted by Sahib View Post
    Why not also send a note to OSHA as a responsible electrical professional?
    Bad idea.

    I said to CYA, not shoot oneself in the foot.
    "Electricity is really just organized lightning." George Carlin


    Derek

  10. #20
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    34,304
    Quote Originally Posted by Sahib View Post
    Either way it should deter the owners to keep an unsafe condition.
    One way of looking at it I guess.

    Remember owner probably knows little about electrical - hears horror stories about others that were caught, fined, had casualties, etc. Decides to call a professional for consultation on what risk he may have.

    Probably is expecting that professional to find problems and make suggestions for solutions, maybe even offer some services to correct such problems. The idea is to avoid being fined by OSHA, and being further investigated in areas other then electrical at same time. Those other areas need addressed as well - but they would likely prefer consultants and not OSHA to point out those issues, which is why they hire them.