    wet-niche fixture
    NEC 680.23(B)(1) does not require a wet-niche fixture to have provisions for a #8 ground if it is a listed low voltage lighting system. However, NEC 680.23(B)(2) still requires a pool rated junction box. It seems unnecessary if there is no # 8 pulled to the wet-niche fixture. Am I reading the code correct?
  2. #2
    Join Date
    Feb 2003
    Pennsylvania
    Posts
    2,489
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Equipment ground connections are done with positive pressure terminals, (not using wire nuts rather set screw types