    I have (2) 100 amp, 3ph, 480V outlets installed in floor. From each outlet there is 1" conduit concrete encased running to each it's own junction box. Those 1" conduits can take only 3#3 awg wires. The panelboard from which (2) 100 amp outlets will be powered, it is 400 ft away. Because of the voltage drop I need to go with bigger wire size, in this case its 2/0 and it cannot be installed in 1" conduit. Now here is my question, I want to install 2" conduit and run 3#2/0 in it to the junction box and from there I need to go with 1" conduit and 3#3. Can I connect #3 and #2/0 together? If it's not allowed, what are my other options?
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,957
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sergiyny View Post
    It is allowed, but you may have a problem finding a crimped butt splice rated for that size difference. Other options include split bolts and Polaris terminals.
  3. #3
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    Also see 314.28 for sizing junction box correctly.
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #4
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, you can connect 2/0 to #3. Are you running welders from these receptacles?
  5. #5
    Join Date
    Jan 2009
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    Am I gonna look like a moron for asking why this would be a factor?
    Pretty common to have one welder using one of two receptacles, convenient locations.
    Derek
  6. #6
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    2,021
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You can also use this to splice them:
    https://www.homedepot.com/p/Blackbur...1-10/100190266
    after splicing cover with rubber tape then plastic tape or use shrink tubing.
  7. #7
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    No. The reason I ask is that welders can use OCPD much higher than wire size and that duty cycle would have a fair amount of impact on wire size. In other words, does he have an actual 100A load at the receptacle?. OP asked if he had any other options; using #2 CU (Still can get 3 in a 1" conduit, using conduit as EGC) back to the panel may be viable.
    Using this calculator:
    http://www.encorewire.com/wp-content...tage_Drop.html
    and the values 480V, Copper, 3ph, 400', and 100A, I get #2 wire is needed.
    Southwire's calculator is not working at the moment as it isnt correctly figuring inputted allowable voltage drop. Using the same specs there I get #1 wire, but at 2.15% VD. I dont see why #2 Cu wouldnt work for his application.