    Is my interpretation of the code correct?
    I’m separating feeders as follows, normal power, equipment power, and life safety/critical power. So as I’m planning pull/junction boxes etc. I’m separating into three systems.
  2. #2
    Join Date
    Jun 2003
    Posts
    6,805
    Quote Originally Posted by PWRUP View Post
    Is it a hospital, nursing home or limited care facility, or an "other" healthcare facility? The requirements are a little different.
    If its a hospital, you don't have it quite right. The life safety and critical have to be kept separate. So they are in separate conduits and separate pull/junction boxes.
    The equipment system could be ran with normal power, although keeping it separate is probably better.
    For a nursing home, the equipment system and life safety branch must be kept separate, and there is no critical branch.
  3. #3
    Join Date
    Oct 2007
    Posts
    10
    It’s a hospital. Not within patient care rooms/areas.
  4. #4
    Join Date
    Jun 2003
    Posts
    6,805
    Then life safety and critical should be separate.
  5. #5
    Join Date
    Jun 2017
    WI, USA
    Posts
    301
    The kva of the system makes a difference as well.
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,331
    Not associated with patient care rooms either?
    Non patient care areas or items associated with them (this is where essential items come in that are not actually in patient care areas)- are not covered by 517.
    Business offices, record keeping, food service, housekeeping, laundry, are a few areas that don't necessarily need to comply with anything in art 517.
  7. #7
    Join Date
    Feb 2003
    Fl
    Posts
    16,819
    Quote Originally Posted by kwired View Post
    You need to read 517.32, all areas of a hospital would be required to comply with this section as well as the other branches of the Essential System whether they are in a patient care area or not.
    Roger
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,331
    Quote Originally Posted by roger View Post
    Roger
    I maybe didn't state this correctly, but understand it the way you said it. Essential system can include things not in patient care areas, they are basically still essential to providing patient care.
    Some of the thing I mentioned like food service, or laundry I suppose can be essential, but maybe are a lower priority then some other items when it comes to just how essential they are and which items one would cut power to first in an extreme situation where you had to make such decisions.
  9. #9
    Join Date
    Feb 2003
    Fl
    Posts
    16,819
    The Essential System is not just basically for providing patient care, the Life Safety Branch would be for everyone inside a hospital including the general public and employees.
    The Critical Branch is more for Patients and hospital functions.
    The Equipment Branch is what it says, and is more inline with article 702 systems.
    Load shedding would be a design and local or state code consideration. During an interruption of Normal Power food service and laundry would need to continue to function for effective hospital operation however, if these services can be catered they could possibly be shed.
    In short, Life Safety and Critical Branches are crash and burn systems, the Equipment Branch is optional to an extent.
    Roger
    Join Date
    Jun 2003
    Posts
    6,805
    If its connected to the essential electrical system (which normally means connected to an essential system transfer switch), then it has to follow the rules for the essential system.
    However, if backup power is NOT required in areas like you mentioned, is possible to put those areas on their own ATS. Lets call it an "optional" ATS since its not required. Then yes, the standard NEC rules would apply instead of 517.