    Ran into a different service panel today. Is this ok.

    This is a 60amp service with the main at the bottom. It has 50amp breaker for the subpanel. Other then not having a clip on the main. Do you guys see any other issues?. Looking for a second opinion.

    Click image for larger version. 

Name:	IM002296.jpg 
Views:	254 
Size:	145.0 KB 
ID:	19317Click image for larger version. 

Name:	IM002299.jpg 
Views:	254 
Size:	149.1 KB 
ID:	19318

  2. #2
    Join Date
    Jan 2018
    Location
    NY
    Posts
    9

    Here's some more photos.

    Click image for larger version. 

Name:	IM002301.jpg 
Views:	200 
Size:	151.7 KB 
ID:	19320Click image for larger version. 

Name:	IM002297.jpg 
Views:	229 
Size:	147.9 KB 
ID:	19321Click image for larger version. 

Name:	IM002304.jpg 
Views:	209 
Size:	149.1 KB 
ID:	19322Click image for larger version. 

Name:	IM002300.jpg 
Views:	210 
Size:	144.9 KB 
ID:	19323Click image for larger version. 

Name:	IM002303.jpg 
Views:	210 
Size:	145.6 KB 
ID:	19324

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,539
    There are a few issues. Looks like there are 3 or more equipment grounding conductor's under the same screw, there are white wires untaped under a breaker and I am not sure what is going on with the main- can't read it and it looks like tape over it for some reason. Also, wires don't appear to be stapled within 12"
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    1,087
    That panel can't be more than a couple of years old. It's a SqD plug-on neutral. What are you doing with it?

    The main backfed breaker doesn't appear to have a hold-down screw.

    There are a lot of breakers in there for a 60 amp main and a 50 amp sub-feed, but if it's overloaded the main breaker should trip so no danger.

  5. #5
    Join Date
    Jan 2018
    Location
    NY
    Posts
    9
    Costumer wants to get up to NEC so inspector will pass it. They bought the small commercial building this way. Most this service runs is a computer and some lights.

    Looking for opinions on this.

  6. #6
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    13,270
    Quote Originally Posted by Dennis Alwon View Post
    There are a few issues. Looks like there are 3 or more equipment grounding conductor's under the same screw, there are white wires untaped under a breaker and I am not sure what is going on with the main- can't read it and it looks like tape over it for some reason. Also, wires don't appear to be stapled within 12"
    I could be wrong, but I think that the white wires are not on the breakers.

    Possible the camera angles make it just look like that.
    "Electricity is really just organized lightning." George Carlin


    Derek

  7. #7
    Join Date
    Jan 2018
    Location
    NY
    Posts
    9
    Quote Originally Posted by jumper View Post
    I could be wrong, but I think that the white wires are not on the breakers.

    Possible the camera angles make it just look like that.
    Yes, you are true.

  8. #8
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    7,173
    Is that big bare copper wire going out of the bottom the GEC, meaning it is going to the grounding electrode making this the point at which the neutral is bonded? If not, then you can't mix the ground and neutrals on the same bars. If the neutral is bonded in that Murray panel above it (with the seal on it), then this is NOT the Service Entrance and the G and N bars would have to be separate.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  9. #9
    Join Date
    Jan 2018
    Location
    NY
    Posts
    9
    Quote Originally Posted by Jraef View Post
    Is that big bare copper wire going out of the bottom the GEC, meaning it is going to the grounding electrode making this the point at which the neutral is bonded? If not, then you can't mix the ground and neutrals on the same bars. If the neutral is bonded in that Murray panel above it (with the seal on it), then this is NOT the Service Entrance and the G and N bars would have to be separate.
    This is the service. That murry box is the for the a-base meter. That is the ground wire to water main.
    Last edited by my88r; 01-11-18 at 07:04 PM.

  10. #10
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,386
    Is that meter a old A base meter, ie only one phase?