    This is a 60amp service with the main at the bottom. It has 50amp breaker for the subpanel. Other then not having a clip on the main. Do you guys see any other issues?. Looking for a second opinion.
    Click image for larger version.
ID:	19317Click image for larger version.
  2. #2
    Join Date
    Jan 2018
    NY
    Posts
    9
    Here's some more photos.
ID:	19320Click image for larger version.
ID:	19321Click image for larger version.
ID:	19322Click image for larger version.
ID:	19323Click image for larger version.
  3. #3
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,133
    There are a few issues. Looks like there are 3 or more equipment grounding conductor's under the same screw, there are white wires untaped under a breaker and I am not sure what is going on with the main- can't read it and it looks like tape over it for some reason. Also, wires don't appear to be stapled within 12"
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  4. #4
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    1,469
    That panel can't be more than a couple of years old. It's a SqD plug-on neutral. What are you doing with it?
    The main backfed breaker doesn't appear to have a hold-down screw.
    There are a lot of breakers in there for a 60 amp main and a 50 amp sub-feed, but if it's overloaded the main breaker should trip so no danger.
  5. #5
    Join Date
    Jan 2018
    NY
    Posts
    9
    Costumer wants to get up to NEC so inspector will pass it. They bought the small commercial building this way. Most this service runs is a computer and some lights.
    Looking for opinions on this.
  6. #6
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,195
    Quote Originally Posted by Dennis Alwon View Post
    I could be wrong, but I think that the white wires are not on the breakers.
    Possible the camera angles make it just look like that.
    "Electricity is really just organized lightning." George Carlin
    Derek
  7. #7
    Join Date
    Jan 2018
    NY
    Posts
    9
    Quote Originally Posted by jumper View Post
    Yes, you are true.
  8. #8
    Join Date
    Jul 2006
    Posts
    7,711
    Is that big bare copper wire going out of the bottom the GEC, meaning it is going to the grounding electrode making this the point at which the neutral is bonded? If not, then you can't mix the ground and neutrals on the same bars. If the neutral is bonded in that Murray panel above it (with the seal on it), then this is NOT the Service Entrance and the G and N bars would have to be separate.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  9. #9
    Join Date
    Jan 2018
    NY
    Posts
    9
    Quote Originally Posted by Jraef View Post
    This is the service. That murry box is the for the a-base meter. That is the ground wire to water main.
  10. #10
    Join Date
    Feb 2007
    USA
    Posts
    5,629
    Is that meter a old A base meter, ie only one phase?