    I had a decision today with a electrican about conductors ampacity correct factors , we a pulling in two #18 thhn conductors for dimming control with the branch circuit conductors do have to Apply the these two dimming conductors to table 310.15B(2). Thanks
  2. #2
    Join Date
    Jan 2009
    Maryland
    Posts
    13,306
    Assuming line voltage and both are CCCs, yes.
    "Electricity is really just organized lightning." George Carlin
    Derek
  3. #3
    Join Date
    Jan 2007
    Posts
    3,049
    Quote Originally Posted by jumper View Post
    More than likely these are the (2) 0-10v leads.
    JAP>
  4. #4
    Quote Originally Posted by jap View Post
    JAP>
    Yes they are0-10v leads
  5. #5
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    18,630
    Quote Originally Posted by jkrauss View Post
    Technically speaking, if they are Class 2 or Class 3, then no derating. But if you have reclassified the dimming circuit as Class 1 to allow you to run them loose in the same raceway with power, you may have to count them. See the post relative to Class 1.