Results 1 to 7 of 7
Thread: Cooling compressor protection
  1. #1
    Join Date
    Nov 2003
    New Jersey
    Posts
    643
    Is it ok just to put an on/off switch at a compressor rather than a local disconnect box that contains a breaker/fuses?
    Tony Shupenko, PE
  2. #2
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,706
    Quote Originally Posted by tonype View Post
    I think you are referring to a condensing unit? Then, yes, a non fusible switch is fine as long as the upstream OCPD is the correct size and type to meet the max OCPD and type on the data plate of the unit.
  3. #3
    Join Date
    Jan 2007
    Posts
    3,769
    That would depend on the type of OCP the unit calls for.
    JAP>
  4. #4
    Join Date
    Jan 2007
    Posts
    3,769
    woops.... texie beat me to it.
    JAP>
  5. #5
    Join Date
    Jan 2007
    Posts
    3,769
    Please lord...... let there be a nameplate on this one....
    JAP>
  6. #6
    Join Date
    Nov 2003
    New Jersey
    Posts
    643
    Quote Originally Posted by jap View Post
    JAP>
    Says "Max fuse or ckt. bkr. fusible/coupe (sic) circuit (HACR per NEC) 15"
    Tony Shupenko, PE
  7. #7
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,663
    JAP>
    "Electricity is really just organized lightning." George Carlin