    Quote Originally Posted by wwhitney View Post
    The two requirements are both in force, it's not either/or. So in your example you'd still need 6" to comply with the section. If your computation came out greater than 6", then the longer length would apply.
    Cheers, Wayne
    No. The 3" length only applies to boxes that are less than 8" in any one dimension.
    Where the opening to an outlet,
    junction or switch point is less than 8 inches (200 mm) in any
    dimension
    , each conductor shall be long enough to extend at
    least 3 inches (75 mm) outside of such opening.
  2. #12
    Join Date
    Feb 2003
    Pennsylvania
    Posts
    2,489
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gadfly56 View Post
    dimension
    That would be about 99% of the boxes in residential.
    How would a min of 6 in not be correct
  3. #13
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,325
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by david View Post
    in my experience, when writing SOP's or regulations, in the event of ambiguity, the latter-most requirement applies. The second sentence overrules the first.
  4. #14
    Join Date
    Apr 2007
    Berkeley, CA
    Posts
    1,795
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    No, they are clearly two different requirements, both of which must be met. Whichever gives the longer length controls.
    Cheers, Wayne
  5. #15
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,325
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Cheers, Wayne
    You need to have a conversation with the inspector who looked at my last home and made me trim the conductors in the 2-gang because they were too long.
  6. #16
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree with Wayne, you cannot ever have less than 6”.