Results 1 to 2 of 2
Thread: CB Sizing and safety factor
  1. #1
    Join Date
    Jan 2018
    LA, Ca
    Posts
    1
    I've got an Inverter 330kW with 3 output legs which I'm using 175A fuses for each leg. Can I use 2/0 in place of 3/0?
    For 175A fuse, 2/0 (195A) provides 11.4% safety factor. Using the ambient temp correction factor of 0.96 (NEC 310.6), I get 187.2A on a 2/0 which gives me 10.69% safety factor.
    Please let me know your thoughts would greatly appreciate also please reference any NEC/UL clause.
    Thanks
  2. #2
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    3,551
    Quote Originally Posted by qwertyRP View Post
    Thanks
    What kind of inverter is this, for PV? What is the system voltage? I am having trouble figuring out a system voltage that would possibly fit with the given information. No one really adds safety factors above a given OCPD size for conductors. In fact, for 800 amps and less, we often have conductors with LESS ampacity then the rating of the OCPD. Note that continuous loads require a 25% safety factor which applies to conductors and OCPD's. What is the load?