Page 2 of 2 FirstFirst 12
Results 11 to 14 of 14
Thread: Amperage readings on three phase 480/277v panel
  1. #11
    Join Date
    Jun 2012
    NW Ohio
    Posts
    995
    Also found laser printers to do this.
  2. #12
    Join Date
    Jan 2016
    PA
    Posts
    5,697
    what do the 100's feed?
    did you check the connections for tightness?
    did you located the vav and see if the heater was cycling?
    a 25 A 480/3 swing is 20 kva, that is a good bit
    34 A almost 30 kva
    that's alot of copiers or printers
    can you measure when the bldg is empty/unoccupied?
    The difference between genius and stupidity is that genius has its limits.
  3. #13
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    1,098
    Quote Originally Posted by Ingenieur View Post
    ...a 25 A 480/3 swing is 20 kva, that is a good bit...
    Is the response rate of the meter accurate enough to trust the numbers?
  4. #14
    Join Date
    Jan 2016
    PA
    Posts
    5,697
    Quote Originally Posted by MAC702 View Post
    if it's not wouldn't the delta A/kva be even higher?i
    https://assets.fluke.com/manuals/87______umeng0800.pdf
    good question
    typ meter
    pg 42
    alot faster than I thought
    wonder if he used min/max function