Thread: Amperage readings on three phase 480/277v panel

  1. #11
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    974
    Also found laser printers to do this.

  2. #12
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,063
    what do the 100's feed?
    did you check the connections for tightness?
    did you located the vav and see if the heater was cycling?

    a 25 A 480/3 swing is 20 kva, that is a good bit
    34 A almost 30 kva

    that's alot of copiers or printers
    can you measure when the bldg is empty/unoccupied?
    The difference between genius and stupidity is that genius has its limits.

  3. #13
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    1,096
    Quote Originally Posted by Ingenieur View Post
    ...a 25 A 480/3 swing is 20 kva, that is a good bit...
    Is the response rate of the meter accurate enough to trust the numbers?

  4. #14
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,063
    Quote Originally Posted by MAC702 View Post
    Is the response rate of the meter accurate enough to trust the numbers?
    if it's not wouldn't the delta A/kva be even higher?i

    https://assets.fluke.com/manuals/87______umeng0800.pdf
    good question
    typ meter
    pg 42
    alot faster than I thought
    wonder if he used min/max function
    Last edited by Ingenieur; 01-12-18 at 10:57 PM.
    The difference between genius and stupidity is that genius has its limits.