Page 1 of 3 123 LastLast
Results 1 to 10 of 23
Thread: 30kva 3phase step up transformer
  1. #1
    Join Date
    Jan 2018
    Loves park,Il United States
    Posts
    2
    I am running power for a sasso k600 extreme Cnc saw and it comes with a 30kva 3phase step up transformer.the saw requires 400volts, the transformers primary side is 230 volts and secondary side is 400 volts. The normal running amps for saw is 80 and a max of 125.so my ? Is what size wire do I need to run to the primary side of transformer and what amp breaker. And then what size wire coming of the secondary side going to saw? I'd appreciate any help
  2. #2
    Join Date
    Sep 2008
    UK
    Posts
    12,009
    Quote Originally Posted by Pratch View Post
    30kVA at 230V is about 75A.
    30kVA at 400V s about 43A.
    Is the 80A for an intermittent duty rather than the NRL?
  3. #3
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Welcome to the forum. Looked up that saw; it's a beast!
    https://www.youtube.com/watch?v=F7z-q2AG38A
    Anyway, look to article 430 for sizing your conductors for the motor. This article may be of some help:
    http://www.ecmweb.com/design/motor-c...uit-conductors
    For the transformer primary and overcurrent protection, see these two articles:
    http://www.ecmweb.com/code-basics/tr...ary-conductors
    https://www.ecmag.com/section/codes-...tors-part-xxvi
    It's too late and I dont do motor/xfmr calcs enough to give you hard numbers.
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,248
    This appears to be a duplicate thread. I posted a response to same question already.
    New member (welcome) your first few posts need to be approved by a moderator before they will show up so be patient, they just want to make sure you are legitimate member and not a robot.
  5. #5
    Join Date
    Jul 2006
    Posts
    8,091
    I closed the duplicate thread.
    Where did the transformer requirement come from? In that video, I see an AC induction saw arbor motor. 400V implies that motor is designed for 400V 50Hz. If you give it 400V 60Hz here, you may damage the motor and the blade because of the change in speed and V/Hz ratio. We don't know how the entire machine is built however, i.e. Maybe there is a VFD on that arbor motor. So if the saw mfr is who told you to use a 30kVA transformer, they likely know more about how it needs to be powered. But if this is coming from someone else as an assumption, I would be very suspicious of it.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  6. #6
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    400 vac at 80-125 A (avg ~100 A)
    I'ld size for 125
    primary 400/230 x 125 = 220 A, CB 250
    the xfmr is likely an auto xfmr (400 - 230) x 100 x sqrt3 ~ 30 kva
    seems like alot ~ 75 hp
  7. #7
    Join Date
    Sep 2008
    UK
    Posts
    12,009
    Quote Originally Posted by Ingenieur View Post
    We are told that the transformer has a primary and a secondary which would mean double wound.
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,248
    Quote Originally Posted by Besoeker View Post
    We didn't get solid confirmation of what kind of transformer it is, just that it has 230 in and 400 out.
    An autotransformer may explain why only 30 kVA rating when it appears the machine driven has even higher rating.
  9. #9
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    an AT has a primary and secondary
    that does mean it has seperate windings
    https://goo.gl/images/WqUjGB
  10. #10
    Join Date
    Sep 2008
    UK
    Posts
    12,009
    How many separate windings are shown?
    Which one is the primary winding and which the secondary?
    Your diagram shows input and output voltages derived from the same winding.
Posting Permissions
  • You may not post replies
  • You may not edit your posts