User Tag List
Page 2 of 5 FirstFirst 1234 ... LastLast
Results 11 to 20 of 41
Thread: GFCI on ungrounded system (system grounding, not equipment grounding)
  1. #11
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by texie View Post
    GFCIs are only recognized for use on solidly grounded systems. I would think if one was applied on an ungrounded system you would have a number of unpredictable issues. Also, since most GFCIs are used in systems of less than 150 volts to ground the systems could not be an an ungrounded system anyway.
    What about my generator, and probably thousands that are like it?
    Connect the 14-30 receptacle on mine to my premises wiring (with proper transfer equip. of course) and now the generator becomes a part of a grounded system - the 5-15 receptacles mounted on it still are usable and do have GFCI protection.
  2. #12
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,325
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    fix quote
    Quote Originally Posted by romex jockey View Post
    Missed that, my bad Al
    Ok, my $.02.....a toroidal coil senses an imbalance , it's not dependent on anything other than that
    ~RJ~
    Exactly, if you have an ungrounded system supplying a receptacle for example, the first ground will cause the GFCI to trip whether or not there is a load connected at the time. This assumes that the grounding connection is of low enough impedance to allow the trip current to flow.
  3. #13
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gadfly56 View Post
    If you have an ungrounded system how do you get any current flow to trip the GFCI until there is a second ground fault? What goes out on one conductor has to come back on the other and there is no other path even with a ground fault for "leakage current" to flow until there is a second ground fault. This is disregarding current due to capacitive coupling - but even current involved in that situation is extremely low and takes a lot of capacitance before it is a problem.
  4. #14
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,325
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Are we talking about a system that is completely isolated from ground (floating), even accidental, or a system that could find earth (ground) on the first fault?
  5. #15
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    TTBOMK grounded means it is intentionally connected at one point (often a neutral conductor) to some reference point that is called "ground" for whatever reason (even if that "ground" is just the frame of a generator), and ungrounded means there is no reference point to other objects of any kind (so floating I guess).
  6. #16
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,876
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    An ungrounded system is completely isolated.
    If you don't think too good, don't think too much.
  7. #17
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,325
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    OK, I withdraw my previous comment in that case.
  8. #18
    Join Date
    Aug 2015
    NY, USA
    Posts
    56
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I've hooked up a world of hot tubs on a two pole gfci w/o a neutral
    I'm fairly sure i was sane at the time......
    ~RJ~
    Ok so this actually answers one of my questions. Don't really need to have a neutral per say... two hots of a grounded system will still allow a GFCI to provide protection. That "path to the source" I am pestering about will allow the leakage imbalance to occur.
    I'm still not convinced leakage current will "exist" on an ungrounded system because it will not have a return path (through earth) to the source.
    To hopefully add some clarity: If an ungrounded system has no faults - meaning there are no unintentional connections between ungrounded conductors and dead metal parts/equipment - and everything is hunky dory... Will a GFCI function if I have wet hands?
    To push it a bit further, in the case where a single ground-fault does exist, and now the system is unintentionally grounded, will a GFCI function as intended?
    It almost seems like a GFCI will only function on a grounded system, or an ungrounded system with a single ground-fault present. Amiright?
  9. #19
    Join Date
    Apr 2006
    Springfield, MA, USA
    Posts
    3,421
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    No system is ever completely isolated from 'ground'. 'Capacitive charging current' has already been mentioned. Even an 'ungrounded' system will have capacitive coupling to ground, and this current can be large enough to cause a significant shock. If you touch a 'hot' conductor then one phase will be grounded through you, and your body will try to carry the capacitive charging current of the other two phases.
    Operating Room isolated ground systems are intentionally small (eg. a single room) to minimize capacitive current.
    In principal a GFCI could protect from shock in these situations, but as others have mentioned the GFCI might not be 'listed' for such use.
    -Jon
  10. #20
    Join Date
    Mar 2003
    Vermont
    Posts
    1,946
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    But this is an interesting bit of electrical theory we've going here.....
    It would appear the contention is that gfci's can't work w/o a path for current to travel
    So if we've an isolation Xformer (floating in space?) , H&N or H&H going through a toroidal to a load , said load side would need a source to loose current to?
    Is that the jist?
    ~RJ~
Posting Permissions
  • You may not post replies
  • You may not edit your posts