    Sounds like a toaster! IIRC, they are required to be ungrounded for that reason.
  2. #32
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gadfly56 View Post
    Not necessarily. Say we have our ungrounded system. You open the Romex at point A and the hot touches a piece of completely UNgrounded steel. You open the Romex at point B and touch the hot to the same steel at a different point; a second fault. Nothing happens, because both points are at the same potential.
    The wire is still faulted to the steel, that is an unintended connection, there just is no current flow to other points of potential from the source at that point all, you have done is join (maybe not a solid connection but is a connection) that conductor to that piece of steel but never developed any place for current to flow. Could be minor amount of current in parallel between both fault point, but as I said probably not that solid of a connection and resistance of those connections probably means the copper wire is still carrying the bulk of what parallel current is present. Still not tripping a GFCi as it won't see this any different then running a parallel set of conductors between two points in a circuit.
  3. #33
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,324
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Yes, exactly so, but I've created two faults without tripping the GFCI. If you argue that they are really the same fault, then lifting either connection should clear the fault. It won't, so I submit there are two faults, not one.
  4. #34
    Join Date
    Mar 2003
    Vermont
    Posts
    1,946
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This might be a great space shuttle experiment .......~RJ~
  5. #35
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,935
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    That is what I have been trying to get across this whole thread. It don't care what is grounded or not, it only wants to see that whatever goes out comes back, if not it went somewhere besides the intended path, that makes it trip.
    And with no deliberate ground in the system there is nowhere for any imbalanced current to flow in the circuit at the GFCI until after the second fault occurs.
    If you had an Equipment (Not) Grounding Conductor, E(N)GC, connecting to the center point of the transformer secondary and to the exposed metal of a load, then you could have imbalance at the GFCI when the first fault between hot and the ungrounded exposed metal occurs.
  6. #36
    Join Date
    Mar 2003
    Vermont
    Posts
    1,946
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Well, up until reading this thread ,i thought planting a Grod for portable gennys was overkill.....~RJ~
  7. #37
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes you created two faults, you did not create an alternate current path that a GFCI will be able to detect.
    Ungrounded system - that alternate path is not a shock hazard to grounded objects until a ground reference is established in the system.
  8. #38
    Join Date
    Aug 2015
    NY, USA
    Posts
    56
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    That's an interesting point... Do you mean that in the sense that it can provide a return path to the source and actually create a path for the unbalanced current to flow? Seems though to a certain degree this would provide a more "reliable" path for the unbalanced current than the current that would otherwise flow from capacitive charging.
    This is all interesting to me. Bonding is critical to have a low-resistance path to the source to clear ground-faults on grounded systems. We want high levels of current to flow to trip breakers. But now it seems grounding, though it does nothing to trip a breaker on a fault, could be beneficial to trip a GFCI considering the little bit of current it requires... Granted choosing a grounded system solely for this reason is unlikely.
    Quote Originally Posted by texie View Post
    GFCIs are only recognized for use on solidly grounded systems. I would think if one was applied on an ungrounded system you would have a number of unpredictable issues. Also, since most GFCIs are used in systems of less than 150 volts to ground the systems could not be an an ungrounded system anyway.
    Which leads me to this...
    By what standard? NEC? Or are you saying only recognized as such by the manufacturer?
  9. #39
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,801
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MechEdetour View Post
    UL 943, the very first sentence. Overview here: https://standardscatalog.ul.com/stan...n/standard_943
  10. #40
    Join Date
    Aug 2015
    NY, USA
    Posts
    56
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ahh ok. I wonder if the motive by that was to limit the scope of the standard or because of this very topic...