User Tag List
Page 1 of 5 123 ... LastLast
Results 1 to 10 of 41
Thread: GFCI on ungrounded system (system grounding, not equipment grounding)
  1. #1
    Join Date
    Aug 2015
    NY, USA
    Posts
    52
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A GFCI receptacle will work on a 2 wire circuit (grounded system) without an equipment ground. It senses current imbalances between the hot and neutral, which when present, it will trip. This makes sense to me and there is no less than a thousand articles on this topic. However, my questions is, will a GFCI receptacle work on an ungrounded system?
    On a grounded system, to my understanding the leakage would go through the body and into the ground to return to the source, and the resulting imbalance would cause it to trip. Technically there wouldn't be a return path through the ground to the source on an ungrounded system. You would be brought to the same potential, and there wouldn't be shock hazard. Am I right here?
    Seems like I answered my question writing this through... To me it seems like GFCIs are useless on ungrounded systems. Actually, can GFCIs even be used on ungrounded systems? There would be no grounded/neutral conductor. Am I going mad?
  2. #2
    Join Date
    Mar 2003
    Vermont
    Posts
    1,893
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I've hooked up a world of hot tubs on a two pole gfci w/o a neutral
    I'm fairly sure i was sane at the time......
    ~RJ~
  3. #3
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,855
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    ~RJ~
    There's a difference between a circuit that does not use the grounded conductor and an ungrounded system.
    If you don't think too good, don't think too much.
  4. #4
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,981
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ~RJ~
    RJ, Your source, the PoCo transformer secondary, is solidly connected to Earth. The OP is asking about a source, and the attached wiring system, that is NOT connected to Earth.
    It's an interesting question.
    I'll take a stab at the theory. With an ungrounded system there is some form of ground fault detection attached to some form of an alarm. The first connection of one leg of the system to ground isn't the one that causes damage. . . the connection of the NEXT system leg is the one that completes a short circuit.
    A person normally would not come in contact with the ungrounded system conductors, but, in the case of a piece of equipment supplied from an ungrounded system through a GFCI receptacle (or breaker), if the piece of equipment is faulted in a manner that connects one ungrounded system leg to the person, that is the FIRST connection of the ungrounded system to ground. No current would flow except for what is necessary for the system ground fault detector. THAT current, passing through the person, if in excess of the 5 milliamp threshold, will trip the GFCI receptacle (breaker).
    Another Al in Minnesota
  5. #5
    Join Date
    Feb 2009
    Posts
    9,855
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MechEdetour View Post
    You wouldn't have any current flow to trip the GFCI on the first fault, so the GFCI wouldn't have any imbalance to cause a trip till after the second fault.
    In a perfect world your ungrounded system would have a ground fault indicator which would light up on the first ground fault and the problem would be corrected before the second ground fault.
  6. #6
    Join Date
    Mar 2003
    Vermont
    Posts
    1,893
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by al hildenbrand View Post
    Missed that, my bad Al
    Ok, my $.02.....a toroidal coil senses an imbalance , it's not dependent on anything other than that
    ~RJ~
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,851
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    And if user(s) ignores the ground fault indicator on first fault GFCI will still protect him if there is a second fault.
    I have a portable generator - 8000 W 120/240 neutral is not bonded to frame - so it is an ungrounded system. It has 14-30 receptacle and two GFCI protected 5-15 receptacles (factory mounted) on the unit.
    Fact it is ungrounded reduces shock hazard some, GFCI still would work if there were a second ground fault.
  8. #8
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,934
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I think it comes down to whether the capacitive charging current is high enough to trip the gfci when the fault is made yes?
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,851
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    I wouldn't say it comes down to only that, but yes capacitive charging current can trip a GFCI - even when part of a grounded system.
  10. #10
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,755
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    GFCIs are only recognized for use on solidly grounded systems. I would think if one was applied on an ungrounded system you would have a number of unpredictable issues. Also, since most GFCIs are used in systems of less than 150 volts to ground the systems could not be an an ungrounded system anyway.
Posting Permissions
  • You may not post replies
  • You may not edit your posts